    firjam's Avatar
    firjam Posts: 1, Reputation: 1
    New Member
     
    #1

    May 6, 2008, 12:06 PM
    Size Wire for amana A/C / Heater unit
    Hello I have a Amana A/c\Heater unit like hotel rooms have and wondering what size wire to use. Here's some spec's that might help

    Cooling Heating
    Amps 3.7/3.8 15.8/14.5
    Watts 805/785 3580/2970

    It's 230/208 60hz 1ph

    And says max fuse 20 amps also has a plug that looks like _ I If this helps
    O

    I'll have about a 40' run from my breaker box to the outlet

    Thanks jamie
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #2

    May 6, 2008, 02:06 PM
    Quote Originally Posted by firjam
    Hello i have a Amana A/c\Heater unit like hotel rooms have and wondering what size wire to use. Here's some spec's that might help

    Cooling Heating
    Amps 3.7/3.8 15.8/14.5
    Watts 805/785 3580/2970

    It's 230/208 60hz 1ph

    and says max fuse 20 amps also has a plug that looks like _ I If this helps
    o

    I'll have about a 40' run from my breaker box to the outlet

    Thanks jamie
    A #12 AWG should be fine
    Then see: NEC 430.109(F): Cord-and-Plug-Connected Motors. For a cord-and-plug-connected motor, a horsepower-rated attachment plug and receptacle having ratings no less than the motor ratings shall be permitted to serve as the disconnecting means for other than a Design E motor and for a Design E motor rated 2 hp or less. For a Design E motor rated more than 2 hp, an attachment plug and receptacle used as the disconnecting means shall have a horsepower rating not less than 1.4 times the motor rating. A horsepower-rated attachment plug and receptacle shall not be required for a cord-and-plug-connected appliance in accordance with 422.32, a room air conditioner in accordance with 440.63, or a portable motor rated hp or less.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wire Size and panel size [ 6 Answers ]

I have a separate small living quarters that is a single room that is about 180 feet away from the main panel. It is going to get another little bed room a small kitchen and a bathroom also maybe a washer. The main panel is a 100 amp meter socket combo. What should I upsize the main panel to? ...

Size of ac unit needed to match a carrrier heating unit [ 3 Answers ]

I had a Carrier natural gas heating unit installed in 2003. Model number 58STA/STX 070 Catalog number 535-80105. My ac unit has gone out and the company I bought the heating unit from has gone out of business. What size ac unit will match the heating unit? Thanks so much!:cool:

What size wire for electric heater? [ 2 Answers ]

I'm hoping someone can help with this question. We are installing an electric wall furnace, 240 volt, 38 amp, 9.2kwh. I was told by the guy at the hardware store to use size 8 wire. The instructions (?? ) that come with the unit don't sat anywhere what size is to be used! Is size 8 wire correct?...

4 wire home service entrance wire size [ 1 Answers ]

Mobile home requires 4 wire electrical service entrance wire. Distance is 160 foot from meter to breaker panel. 220V service. What size wire do I use? Can I use diff. size for neutral and ground?


View more questions Search