    GFI Open ground?
    I recently install 3 GFI receptacles outside. They are wired correctly with ground attached in a 3 wire (copper) system. The boxes I used are outdoor plastic boxes. So the ground wire does no good being attached to this box. Why does it show open ground on my tester? Thank you
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    May 4, 2008, 07:22 AM
    Either the tester is faulty, which I doubt, or the bare or green equipment ground wire is not connected proper someplace.

    The ground wire must connect to each of the green screws on each outlet, all must be spliced together, so that there is a path back to the grounding or neutral bar back at the panelboard.

    Be sure to note at the panel if there is only one bar for both neutral whites and green/bare grounds, or is there a separate bar just for the green/bare grounds. If the main breaker is in that panel, then white neutrals and grounds will be together. If there is a separate ground bar, then only white neutrals are on one bar, and green/bare grounds are separated on another bar.

    If you extended these new outlets from an existing circuit, then there is a problem with the grounding of this circuit.
    lour's Avatar
    lour Posts: 2, Reputation: 1
    New Member
     
    #3

    May 4, 2008, 09:22 AM
    First of all, thank you very much for your quick reply. And I took your advice and checked the existing house circuit and found that the builder did not hook up the ground wire to a previous receptacle on this circuit. That does surprise me. When we bought the house. I changed the receptacles over from the ivory colored ones to white and found in each receptacle ground wires were not connected. I could see by the end of the wire they were never hooked up. I thought this was part of electrical inspections. Anyway, many thanks for your help!
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    May 4, 2008, 10:28 AM
    If your builder took that serious of a shortcut I would check out everything else he did!

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Two Lights on One Switch, Power to Light, Open Ground [ 9 Answers ]

I'm struggling with a pair of lights in a small workroom. The circuit comes in and feeds the two lights (on one switch) and three outlets from the 2nd (middle) light. I figured out that I needed to make two hot whites leading to the switch from the first light so I made both of the whites hot...

Outlets showing open ground [ 6 Answers ]

Hello, I started having an issue last night with my electric. All of the sudden my computers ups started beeping like crazy and I noticed it also showed an electrical fault. I tested the outlet with a 3 pronged tester and it showed an open ground. I also found 7 more outlets in the...

Open Ground showing on grounded outlet [ 2 Answers ]

Replacing an outlet I attached the ground wire to the ground wire coming out of the wall box. The test shows an open ground, so I did it again. Same results. The ground wire inside the box is twisted with another ground wire and both appear to be solidly connected coming out. All other outlets...

Can an open ground reading on a grounded circuit mean a 240V line? [ 2 Answers ]

Hi, folks - wondering if someone can help me out. I'm getting an "open ground" reading on a wall outlet which is being fed by 12/2-grounded romex cable. The cable is grounded at the panel, so I'm not sure why I should be getting an open ground reading. This line is for an electric baseboard...

Open ground when neutral not touching ground [ 3 Answers ]

Hi, I was moving around a room and noticed my wife wanted her desk elsewhere. I decided to, since she would have her computer on it, check the outlet she would be moving to. It seemed old so I changed it. I noticed before I changed it that with my GFCI tester, all sockets on this circuit were...


View more questions Search