    May 3, 2008, 01:33 PM
    Tempstar dual capacitor
    I have replaced my motor on my outdoor unit but can't remember how the wiring goes back to dual capacitor, I have three wires, brown with red mark, red and white. Which goes to common and fan and which terminal does the other wire go to?
    letmetellu's Avatar
    letmetellu Posts: 3,151, Reputation: 317
    Ultra Member
     
    #2

    May 3, 2008, 01:57 PM
    Well the first thing is that you should have bought a new capacitor, one that the motor that you bought requires. You do not have to buy a dual capacitor. Depending on the HP of the motor the capacitor may be something like a 7.5 uf 370 volts.

    Now about the wiring, you only have three wires so if you connect to the old capacitor that you already have, the brown will go to the post on the capacitor marked fan, the white will go to the center post, or the one marked com, this post should have at least one yellow wire on it already that is coming from the contactor. The third wire will go to the contactor, on the pole that the yellow wire is not connected to.

    If you do buy a new capacitor this is how the wiring will go, after removing all of the wires going to the old motor you will then connect the brown wire to one side of the new capacitor. The white wire will go to the same side of the new capacitor. The black wire will go to the side of the contactor marked T-1 or lets say the top terminals on the contactor.
    You then will have to install a wire from the side of the contactor marked T-2 or lets say the bottom side of the contactor, this wire will then connect to the side of the new capacitor opposite where the brown wire is connected.

    Black to T-1 on contactor
    Brown to one side of capacitor
    White to other side of capacitor
    Jumper from same post white wire is on to T-2 on the contactor.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Start capacitor/ run capacitor info [ 3 Answers ]

OK I think I have narrowed my problem down to either a run capacitor or my start capacitor My fan on top of my unit runs but the compressor will hum for about 3-5 seconds every 5 minutes or so . Is it possible for my duel run capacitor to let the fan run but not let the compressor run, or is...

Dual capacitor to two capacitors wiring [ 10 Answers ]

I am trying to chang my fan motor and the new motor calls for a different capacitor... the wiring is obviously different. I took the old wires off the old capacitor and wired in the new capacitor as directed on the new motor. Leaving the old one just for the compressor wired the same as it was. The...

Tempstar furnace [ 1 Answers ]

My tempstar furnace burners light and then turn off, light and turn off, they cyle about every 3-5 seconds, when they should burn continuously. What is the problem?

Tempstar 5000 [ 1 Answers ]

I have a Tempstar 5000 A/C unit and would like to know the condenser size It's model # is ca5536uka1 so should I assume it is a 3 ton unit? Thanks Erik

Tempstar 5000 [ 3 Answers ]

I have changed the coil because it looks like it had a spark or got hot because there was black soot on the power terminals so I replaced it but it still doesn't work. When you turn it on there is a small hum the magnets are not being pulled in, when you push them in humming gets louder from the...


View more questions Search