    Blower ignites but goes out before fan comes on
    :mad:
    On a nordyne-cmf80-pg-di-n lp gas heater what is causing the blower to ignite,then turn back off before the fan system ingages??
    N0help4u's Avatar
    N0help4u Posts: 19,823, Reputation: 2035
    Uber Member
     
    #2

    Mar 22, 2008, 09:38 AM
    Sounds like a bad thermocoupler
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #3

    Mar 22, 2008, 11:32 AM
    Trying to run the furnace at a reduced temperature.

    The burner starts, heat exchanger warms up and just before/as the fan starts the burner cuts out. The burner immediately starts the purge/start cycle but by the time the burner starts the heat exchanger has cooled enough to stop the fan so it just does the same thing again.

    Does the above sound like your problem?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Blower runs before furnace ignites [ 2 Answers ]

What makes your furnace blower come on first before your ignites

York Model P1CK, ignites then locks out after 5 cycles [ 1 Answers ]

Hello, I have a York P1CK D1N06401A natural gas furnace in an upflow orientation. The equipment is 11 years old and has all original parts and controllers. The LED fault code is 8 flashes which, according to the Installation documentation ("Indicates that the flame has been lost 5 times during...

3A fuse blowing after furnace ignites [ 5 Answers ]

'Working on a 10-yr old Goodman GMP050-3. A/C is okay, but no heat. Circuit board and ignitor were just replaced and the flame sensor has been cleaned. The unit comes on, status light solid, ignitor glows, gas comes on and ignites, but after 2-3 seconds the 3A fuse on the board blows.

New thermostat, Furnace ignites fire but no heat [ 3 Answers ]

Hi My furnace and thermostat was working fine until two weeks ago. So I replaced the thermostat and the heat started working for the first day then it stopped. I tried to turn up the degrees on the thermostat and I checked the furnace. The electric ignitor was working fine and there was fire...

Fan Blower doesn't come on in Fan,heat or cool [ 2 Answers ]

Yesterday I turned on my heat(coil in air handler) and everything worked fine. Last night I turned it on again and the fan wouldn't come on no matter where the switch was: fan only, heat or air. I made the appropriate temp changes for heat/air. There is a humming noise coming from the heating coil...