    Venting a toilet
    I had a plumber in to redo my drain line. He said that because the vent is on the outside wall of the house it is not to code and must be moved into the house more so that it is not on the edge of the roof. I have never heard of anything like that. Does anybody know how far away from the edge of a roof a vent must be?
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #2

    Mar 20, 2008, 12:58 PM
    This guy is just looking for work. Tell him to forget it. Many vents are on outside walls but they can be changed by adding two 90 degree elbows inside the attic before it reaches the roof. If it ain't broke don't pay to have it fixed. I'd keep what I have if there is no sewer gas problem in the home.
    amricca's Avatar
    amricca Posts: 851, Reputation: 92
    Senior Member
     
    #3

    Mar 20, 2008, 02:43 PM
    Just checked the International Plumbing Code and the only thing I see code wise is the height above the roof, proximity to any windows or intakes and the distance to any neighboring structures, which is 5 foot minimum. Nothing about it not being allowed in an exterior wall.
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #4

    Mar 20, 2008, 03:24 PM
    Amricca is right... no codes saying can't run vent on the outside of the house as long as the pipe terminates above the roof at least 18" to 24" above the roof line. There are restrictions in terms of windows, especially skylight type windows that open, but as was stated by Amricca... most requirements are met if vent at least 5 feet away from any window.

    Permdog... does this vent run above the roof.. Or does it terminate under the eaves..? This vent pipe we are talking about is on the OUTSIDE of house...yes? Plumbing inspectors frown on running vent pipes outside of house... but will allow as long as rules are met... Let us know... Mark

    .

    .

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Venting toilet with 1/8 bend? [ 3 Answers ]

Looking at the attached, I know an 1/8 bend is 22.5 degrees, does this mean the vent would be 22.5 degrees off center right? This configuration can utilize a clean-out and may serve as a vent for shower and vanity? What if I put in a wye just downstream from wye shown to pick up 2" from shower...

Toilet Venting [ 4 Answers ]

I was hoping you could help me with a general question about my 2nd floor toilet operation. My TOTO toilet creates a gurgling and/or choking sound when flushed. I have research this problem and found that it maybe cause by improper venting. I also conducted a 2-gallon bucket test and got the same...

Venting a toilet [ 1 Answers ]

Hello, My problem is this; I'm installing a shower and a toilet side by side. From the main stack, the shower sits closest, then the toilet. Some time ago, a plumber friend of mine told me I could vent my toilet through my shower vent. My shower drain is to be 2" PVC, and the toilet 3" PVC. Both...

Venting a Toilet [ 4 Answers ]

Running a 4" ABS. Upstream about 5' will be a 4X4X2 Wye for the tub with it's own vent, plus another 4X4X2 Wye for the washer with it's own vent. The main's stack vent will be about 6' downstream. I believe that meets code since there are 2 vents upstream of the toilet, am I right? Also, is...

Upflush toilet venting [ 2 Answers ]

I am in the process of finishing my basement and decided to use a Saniflo Saniplus macerating pump unit for lifting wastewater from a sink, toilet, and shower into the existing 4 " drain line (the 4" drain exits the basement approximately 4' from the basement floor). The force main is the easy...