    Limit cicuit lockdout
    Hey,
    I have a Payne furnace model PG8MAA042090.I Had A "Hot surface Ignitor go out,so I replaced it.I though as long as I am doing this why not replace the thermostat.I bought a "Hunter 44860 touch screen model" and replaced that along with my HSI.But Now The furnace shuts off before reaching the set thermastat temp.What happens is the heat goes out the blower stays on,I start getting a 33 error code (Limit Circuit Fault)then after 3 minutes the blower shuts off and I get a code 13 "Limit circuit lockout"Code list says it will reset after 3 hours.It never did this before.Any help would be apreciated.Thanks,Blue. It was fine before the HSI and thermostat.Could the timer (The thingy that calculates energy usage )in the thermostat be messing things up?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Mar 15, 2008, 05:05 PM
    To isloate the problem reinstall your old thermostat just like it was. Then we will find out if it is the furnace or the new thermostat.

    BTW your unit is going out on the limit circuit for some reason.



    33 LIMIT CIRCUIT FAULT - Indicates a limit, or flame rollout is open. Blower will
    Run for 4 minutes or until open switch remakes whichever is longer. If open
    Longer than 3 minutes, code changes to lockout #13. If open less than 3 minutes
    Status code #33 continues to flash until blower shuts off. Flame rollout switch
    Requires manual reset. Check for: - Restricted vent
    - Proper vent sizing - Loose blower wheel - Excessive wind
    - Dirty filter or restricted duct system.
    - Defective blower motor or capacitor. - Defective switch or connections.
    - Inadequate combustion air supply (Flame Roll-out Switch open).


    13 LIMIT CIRCUIT LOCKOUT - Lockout occurs if the limit or flame rollout switch is
    Open longer than 3 minutes

    A educated guess about all of this is that you might have wired your new thermostat wrong.

    ARE all your ducts open and the return air filter clean?
    the blueberry's Avatar
    the blueberry Posts: 3, Reputation: 1
    New Member
     
    #3

    Mar 15, 2008, 06:13 PM
    I reinstalled the mecruy thermostat it works fine now.I wired exacly like the book said.I only have for wires.It was ptreaty self explanitory.It sucks cause I like that model.Easy to program see and everything.I know it was right on the wireing .I checked it 3 times.Yes I'm anal.I ran the mecry tstat for an hour with no shutdown.The Hunter made it mabe 20 minutes before the burner shut down.I checked the web after posting and found the Hunter can do that.It has something to do with the way it calculates the amount of heat it will need and the way it asks.I was to tired to go into detail.Any hints on a replacement.I really want that programability for summer air season?Lowe's carries a Honneywell for around 99. US,They anybetter?Or do you think the thermostat was just irrating a already bad part?Thanks,Your worth a thousand.LOLOL.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Mar 15, 2008, 07:12 PM
    If the truth hunter thermostats are junk. Get Honeywell.
    the blueberry's Avatar
    the blueberry Posts: 3, Reputation: 1
    New Member
     
    #5

    Mar 15, 2008, 07:20 PM
    Ill give it a shot tomorrow.Thanks for your help.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Fan Limit [ 2 Answers ]

I have an older furnace with a Honeywell fan limit switch. The unit ignites, heats up and then the fan comes on normally. When it gets to the proper temperature the heating unit shuts down and the fan continues to run, as it should, as the unit cools down. The problem is that the fan doesn't shut...

Cicuit breaker [ 3 Answers ]

What is the function of circuit breaker ?

Going up on Limit? [ 3 Answers ]

Hello, I have a couple questions about my furnace and more specifically my Fan & Limit control. Riello 40 Oil Furnace Honeywell L4064 Fan & Limit Control Recently, at the time of the annual furnace inspection and cleaning, the technician who came to look at the furnace said that my furnace...

What's the Limit? [ 4 Answers ]

I currently have an nVidia GeForce 5500 PCI graphics card in my PC. I have no AGP slots. My PC is a Compaq Presario SR1120NX. The graphics card works fine, but I know it's outdated. I want to move up to something that delivers more punch, but am having trouble finding anything. I've looked at...


View more questions Search