Mar 12, 2008, 05:06 PM
|
|
Rough waste pipe locations
Re-plumbing my house in NH and wondering what the standard drain/waste pipe locations are supposed to be for kitchen sinks, bathroom vanities, toilets etc... From the research I've done I need a 3" toiliet drain, 2" reduced to 1 1/2 for the sink and tub drains, and 2" for a shower stall. What are the heights recommended for the sink drains and the distance for the toilet drain? Thanks.
|
|
 |
Junior Member
|
|
Mar 12, 2008, 05:07 PM
|
|
Also what are the requirements for cleanouts on the 3" drain in the basement?
|
|
 |
Senior Plumbing Expert
|
|
Mar 12, 2008, 05:26 PM
|
|
Hi John:
3" to toilet drain....yes.
2" reduced out of p-trap to 1.5 inch for tub
2" NOT reduced for shower p-trap
2" reduced to 1.5 " for sinks
Kitchen sink drains at about 15" to center off finish floor (to acommodate disposal).
Lavatory sink drain at 18-20" off finish floor
Toilet is 12" off rough wall to center of pipe and a minimum of 15" off side wall.
Cleanouts for 3" are required at new connection to main pipe (dandy cleanout (see pic.)), at every change of direction (within reason), at end of run, and at base of stack if going vertical waste stack.
Get back to me if need more info... Mark
|
|
 |
Junior Member
|
|
Mar 12, 2008, 05:50 PM
|
|
Would I be safe to run 2" vents for all the drains, excluding the toilet which would be a 3" stack? Also, can I just reduce the 2" for the sinks in the wall to 1 1/2?
|
|
 |
Senior Plumbing Expert
|
|
Mar 12, 2008, 06:08 PM
|
|
Very safe to run 2" vents for all drains...including toilet, except you say 3" stack vent for your application.. that is fine, too.
I wanted to add that you can run 2" drain/vent for a lavatory sink (stub out 2" to sink and then reduce to 1.5 inch pipe/trap) "as a wet vent for a toilet if the connection for sink drain made into 3" toilet drain pipe within 8 feet of the toilet... that make sense? That means that you do not have to run separate sink vent and then separate toilet vent... they can be combined.
Otherwise, add a full size 2" cleanout inline and then can reduce to 1.5" for sinks... Let me know if/when you need more.
.
|
|
 |
Junior Member
|
|
Mar 12, 2008, 06:42 PM
|
|
I understand for the wet vent of the bathroom sink... and it will be no further than 4-5 feet from the stack so that'll work. How do you recommend venting the tub drain?
|
|
 |
Senior Plumbing Expert
|
|
Mar 13, 2008, 03:53 AM
|
|
Hey John... tub being run 2" waste then reduce to 1.5" out of the ptrap to tub waste and oveflow assemnbly of tub. The vent is taken off the 2" drain line with fitting (sanitary tee) rolled above center line within 6 feet of the tub p-trap...then tub vent runs to join the other vents in bathroom.
All vents must connect...at a minimum...at least six inches higher then the flood level rim of the highest fixture in bathroom..In this case (as in most bathrooms), the highest is the sink. A 2" vent can pick up all the bathroom vents and then run that to vent stack and connect at floor above OR at existing attic vent OR out the roof 2" by itself.
Hope that made sense.
If this helped please RATE THIS ANSWER. Thnak you... Mark.
Get back with any more questions... anytime.
|
|
 |
Junior Member
|
|
Mar 13, 2008, 05:34 AM
|
|
What do you mean by the term "rolled above center line"?
|
|
 |
Senior Plumbing Expert
|
|
Mar 13, 2008, 05:37 AM
|
|
Vents need to roll above the center line of a horizontal drain line... if they rolled off drain line only at center, then when waste rolled by the stream would cover the vent fitting instead of mixing with the air from it. That make sense..
|
|
 |
Junior Member
|
|
Mar 16, 2008, 05:14 AM
|
|
If you were to use the analogy of a clock... horizontal would be 3 or 9 o'clock. Above center line would be like 1 or 11 o'clock?
|
|
 |
Eternal Plumber
|
|
Mar 16, 2008, 05:23 AM
|
|
 Originally Posted by johnwi3
If you were to use the analogy of a clock... horizontal would be 3 or 9 o'clock. Above center line would be like 1 or 11 o'clock?
That's correct. All dry vents must be rolled upright or on a 45 degree angle when taken off the main. If this vent will be washed by a fixture, say a lavatory, then the fitting does not have to be rolled up but connects in the usual way.
Good luck, Tom
|
|
 |
Junior Member
|
|
Mar 16, 2008, 06:50 AM
|
|
You guys have been a great help and I thank you much... so here's another question. I have 4" cast iron drain under my slab in my basement, it runs from the front where the original stack was to the rear then out to the septic tank. I am in the process of digging up the old cast iron to replace it with 4" PVC, I want to make a stack in the front and rear of the house to accommodate two separate baths. I plan on making the connection to the cast underground and tee'ing up right where it enters the foundation for the first stack, then running the PVC to the front of the house and have another 4" stack come through the floor. The stacks will be reduced to 3" for the baths and other fixtures... My question is how can I design the system so it can be pressure tested when its done? The "tee" connection will be underground approx. 1.5 feet and that seems to be the only area where you could put the plug to test the whole system. Kind of confusing?
|
|
 |
Eternal Plumber
|
|
Mar 16, 2008, 07:13 AM
|
|
.. My question is how can I design the system so it can be pressure tested when its done?
You don't do a pressure test on drainage. You perform a static test by capping off all fixtures , installing test or clean out tees, See image) at the base of the stacks, inserting inflatable test plugs, (see image) in the tesr tee to make the system water tight. You then take a hose up onn the roof and fill the stacks to overflowing and let them set for 8 hours before calling in a inspection. That's how we test our drainage. Good luck, Tom
|
|
 |
Junior Member
|
|
Mar 16, 2008, 10:01 AM
|
|
Do I need to have any type of fitting such as a tee under the ground where the connection to the main drain is going to be or can I test each stack separtely?
|
|
 |
Eternal Plumber
|
|
Mar 16, 2008, 10:18 AM
|
|
 Originally Posted by johnwi3
do I need to have any type of fitting such as a tee under the ground where the connection to the main drain is going to be or can i test each stack separtely?
Since this is a remodel you don't wish to test the entire house. On each vertical stack vent before it goes under ground install a test tee and fill the stacks individually. Good luck, Tom
|
|
 |
Junior Member
|
|
Mar 16, 2008, 12:57 PM
|
|
What about the main drain that will be buried under the floor? This will be 4" that 2 3" stacks will come off, 1 in the front and 1 in the rear.
|
|
 |
Senior Plumbing Expert
|
|
Mar 16, 2008, 01:07 PM
|
|
Hi John;
When you come out of floor 4" at both stacks, install the dandy cleanout I showed you in post #3...then reduce to 3" for bathrooms. At the base of the 3" stacks, should also install 3" dandy cleanouts... unless the 4" dandys are close by then can probably use them. If any question at all.. install another cleanout... they never hurt anything and boy can they help if blockage occurs!
Also, no tee fitting off underground waste pipe... wyes.. ok, wye/1/8th bend or combination wye1/8th fitting OK... but NO TEES.. ok?
Any other questions?
|
|
 |
Junior Member
|
|
Mar 16, 2008, 01:18 PM
|
|
I think I got it. You guys rock. Thanks a bunch.
|
|
 |
Senior Plumbing Expert
|
|
Mar 16, 2008, 01:47 PM
|
|
Anytime Johnwi3
Thank you... Mark
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Un-used 3 inch waste pipe
[ 2 Answers ]
My house had an option of a second bathroom. The original owner did not go for this option & the plumber put cement in the hub of a 3 inch cast iron waste pipe. I want to now add the second bathroom and I need to use this pipe since it is in the right location. Running a new pipe is out of the...
A new waste pipe - is this right?
[ 3 Answers ]
I added the waste pipe located at the front of the attached picture 1... The vertical arm on the left of the main waste pipe was already plumbed for future connection as was the vertical pipe on the right coming down from the second floor (you can see it in picture2).
Can anyone verify that this...
Replace Lead Pipe from Toilet to Hubless Waste Pipe
[ 3 Answers ]
My house is a craftsman style house from 1912 in Oakland, California.
I have a big hole in a 24" horizontal lead pipe that bends at 90 degrees and connects the only toilet in the house to the hubless waste pipe.
How do I go about removing the lead pipe? (What tools do I need and what type of...
Waste pipe? Removal
[ 2 Answers ]
Im not sure what I have here, but I am trying to cap it.
Here's what the configuration is. My house was originally built in 1967.
In my basement I have what appears to be a 2" dia. galvanized pipe protruding about 10" out of a 4-41/2" dia. iron pipe. There is a threaded coupler at the top of...
125mm waste pipe
[ 1 Answers ]
Can someone tell me if the drainage pipes from the kitchen sink are supposed to join directly onto the same 125mm waste pipe that the toilets are also connected to? Iam in the process of refurbishing my flat and have come across such a setup.
Does anyone know if this is legal? Surely there must...