    Goodman gmp 150 blower not turning on
    Last Sunday night, returned home from weekend trip to a cold house and the fire alarms going off. After shutting the alarms off, I went to the furnace to see why it wasn't working. The breaker was off at the box. I reset the breaker and the furnace started back up - inducer motor, then glow, then ignition. When came time to start the blower, the circuit board triggered the motor to start, but there was a blue flash in the motor and the circuit breaker blew.

    Bad motor. Replaced the motor (dual post\fans 3/4 HP). Had to move stuff around quite a bit to get the squirrel cages out of the box. Hopefully didn't mess up wires.

    After getting everything installed, turned on - inducer, then glow, then ignition, then nothing until high temp sensor shut off the furnace. I bypassed the circuit board completely and am running the furnace blower all the time from outside power. The furnace works good, except the blower from the circuit board.

    What could I have missed on the reinstallation. BTW, the connectors on the cables on the bad blower are black (burned looking) as is the capacitor (which is above the blower connectors on the board). I did replace the capacitor also.

    Does this sound like a bad circuit board? What else could I look at before replacing the board. Again, everything appears to function properly, except turning on the blower.

    Thanks
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Mar 11, 2008, 01:55 PM
    ((came time to start the blower, the circuit board triggered the motor to start, but there was a blue flash in the motor and the circuit breaker blew.))

    You may have burnt the relay on the board for the motor.
    jwill51's Avatar
    jwill51 Posts: 2, Reputation: 1
    New Member
     
    #3

    Mar 13, 2008, 09:46 AM
    Replaced the circuit board and the blower works fine. I assumed that I would need to do this, but wanted confirmation.

    Thanks HVAC1000

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Goodman furnace turning off [ 23 Answers ]

I have a goodman GMNT080-4 furnace. It's about two years old. When the thermastat first turns it on, it runs great... for about an hour, then it just stops, even though the thermastat is still saying system on. If you reset the thermastat, sometimes it fires right back up again, but only...

Goodman furnace not working after turning off and back on [ 6 Answers ]

Hello, we purchased a Goodman furnace June 2006. When we turn off the furnace, and turn it back on, the furnace does not work. I've left numerous voice mail and text messages for Air Kings in Columbus, Oh and they do not return my call. This is the company that installed the furnace. It is 30...

Goodman furnace gmp [ 7 Answers ]

Ok. I can turn the thermostat to 72 and it will stay on 64 with the fan blowing constant. Burners aren't firing. On the control board for the furnace, there is a trouble shooting light that blinks to tell you what is wrong. It blinks four times which indicates an "Open Limit Switch", and it tells...

Blower motor wiring on a Goodman GMP [ 2 Answers ]

I have a Goodman GMP forced air furnace running on natural gas. It is about 5 - 6 years old. It recently went out. The draft inducer would come on and the igniter would glow but then it would shut down without opening the gas valve. I checked and found that the board was never sending a...

Goodman GMP Problem [ 2 Answers ]

I have a Goodman GMP 100-4 running on propane The last week or so, has seen some intermittent operation. The draft inducement motor comes on but at times no ignition occurs. Vacuum manually applied to the vacuum switch results in ignition taking place. Inducement motor area has been cleaned out....


View more questions Search