    I have a York Diamond 90 that I am trying to figure out what is causing an issue with it.
    I seem to have an issue with a lot of condensation building up in the inducer assembly. There are three tubes that feed the condensate trap however it tube from the inducer drain is the one that is draining the most water(the bottom part of the inducer). All the tubes and trap seem to be clear. I would assume the condensate pan drain should have the most water but there is very little. Could there be a blockage in the vent pipe? Any help would be greatly appreciated.

    FYI, I can hear the water sloshing around and the inducer motor whines as the water builds up. I just had the inducer motor changed about a month ago.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Mar 9, 2008, 11:12 AM
    Vent could be blocked OR snow if the pipe is to low.
    Make sure all drains are clear.Make sure all vent pipe areas are clear of debris.
    If you just had the inducer replaced it might have been because of the water. If you do not find the problem you will need to call a pro or you might be buying another inducer.
    T-Top's Avatar
    T-Top Posts: 1,871, Reputation: 100
    Ultra Member
     
    #3

    Mar 9, 2008, 05:53 PM
    If the system is working no worries, the splashing sound around the inducer wheel is normal. You may have more condensation on cooler days than the warmer ones.
    bpp's Avatar
    bpp Posts: 9, Reputation: 1
    New Member
     
    #4

    Mar 10, 2008, 08:57 AM
    Quote Originally Posted by T-Top
    If the system is working no worries, the splashing sound around the inducer wheel is normal. You may have more condensation on cooler days than the warmer ones.
    Yea, everything seems to be working fine now. I took a shop-vac to all the hoses, pipes,etc. The unit has a horizontal vent pipe so I believe the proper design of my system should have been built with a tee at the horizontal part so that condensate in this part would flow off to the drain. The installers got lazy or just didn't care I guess, sigh.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #5

    Mar 10, 2008, 09:12 AM
    Good deal. Glad you got it working. I believe water in the inducer creates a load on the inducer motor that is not supposed to be there. They are designed to push air not pump water.
    bpp's Avatar
    bpp Posts: 9, Reputation: 1
    New Member
     
    #6

    Mar 10, 2008, 09:38 AM
    Quote Originally Posted by hvac1000
    Good deal. Glad you got it working. I believe water in the inducer creates a load on the inducer motor that is not supposed to be there. They are designed to push air not pump water.
    Quick question. When I got the inducer changed, I believe the installer should have used RTV sealant on the vent pipe as well as probably to the gasket that attaches to the condensate pan. Am I correct and should I go back and put this on?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Furnace inducer motor [ 5 Answers ]

What are the implications of a furnace inducer motor drawing high Amps?

Hvac inducer [ 2 Answers ]

What does an inducer do on a hvac system. Is it a problem if the gasket is bad on the inducer?

Problem with inducer motor which just went out. [ 3 Answers ]

Hello everyone, this is my first question on this forum. I hope that some of you can help me out with this query, as I'm literally out in the cold right now. My inducer motor just went out on our central a/c heating unit. It's a York rooftop model. I am wondering if someone could guide me as to...

Replacement Inducer [ 10 Answers ]

What is the replacement inducer for a horizontal Carrier 349MAV036075 furnace? Currently, the inducer blower is a Fasco 7162-3136. The Fasco website suggests the A142 but with the inducer mounted blower upward on the furnace the condensation drain nipple on the inducer is at the 9 o'clock...

Inline inducer [ 3 Answers ]

The room over my garage is the furthest room my furnace. It is colder in the winter and hotter I the summer than the res of the house. I am thinking of buying an inducer to boost air flow. Should I install the one with the heater as well? What happens in the summer with air conditioning? Where is...


View more questions Search