    New Marathon Water Heater and Desuperheater + circulation?
    I’m in the process of installing a new Marathon water heater, model 8545, which will be coupled to the desuperheater of my geothermal system. The propane water heater that this new unit is replacing has a return line from the far end of the house from one of the bathrooms. This return line allows the hot water to circulate so that this remote bathroom has hot water without waiting 5 minutes for the hot water to reach it. The current configuration that works very well has a ¾ inch copper hot water supply line to this bathroom and tapped into this line at the bathroom end is a ½ line that returns to the hot water tank through a gate-valve and check valve. It attaches to the lower end of the propane hot water tank to a fitting that was supplied for hydronic heating. The Marathon heater does not have this fitting.

    Here are my questions,
    1. Do I need the check valve in the system?
    2. Can the return line be attached to the cold side of the Marathon water heater? It has a dip tube.
    3. Some circulation systems tap in to the tank drain valve end, but this is the return point for the hot desuperheater. Not sure if this would work for the return because of this.


    Thanks,

    Eric D
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #2

    Mar 7, 2008, 05:20 PM
    Eric... Hi.

    Let's see if I can help. BRB
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #3

    Mar 7, 2008, 05:30 PM
    You need the check valve in system.

    You can tie into cold water inlet to marathon water heater as long as check valve is above connection into heater and pointed in right direction ;) (may need to add expansion tank here between check valve and cold inlet to water heater.. but let's talk connections first).

    Some systems do tie into the boiler drain at base of water heater... need to remove boiler drain to do this. I think the marathon has a union type fitting.. so can be done.. but sounds like you have other plans for that tapping?

    Cold water connection should work.

    BUT for best outcome here... do not hesitate to call the number marathon heaters provided (in instruction sheets) to ask any question regarding their heater.

    THEY have supplemental specification sheets available that will tell you exactly how marathon heaters wants you to pipe this AND KEEP their warranty in effect.

    Check out Marathon Water Heaters for numbers/information... get back to us.

    Is your recirc. Line insulated? Let me know your thoughts... Mark
    Eric D's Avatar
    Eric D Posts: 98, Reputation: 4
    Junior Member
     
    #4

    Mar 7, 2008, 06:00 PM
    Quote Originally Posted by massplumber2008
    You need the check valve in system.

    Is your recirc. line insulated?? Let me know your thoughts...Mark
    Hi Mark,

    Thanks for your input. Yes, the recirc line is insulated. It has worked well for the last 9+ years. I have found that every bit of air needs to be out of the line for it to work properly. When I have opened the water lines for changes or what have you, the return will stop working until I bleed the air out a few times. Thanks for pointing out the Marathon website. I've been there a number of times even before buying my unit.

    Oh, I had the model number wrong in my first post. It is a MR85245B. The unit is about 124 lbs empty. Not to bad for 85 gallon tank. I managed to get it down my basement with a two wheel hand truck. I'll let you know how it works with the new unit once I complete the installation. With a little luck that should be tomorrow.

    Regards,

    Eric D
    Eric D's Avatar
    Eric D Posts: 98, Reputation: 4
    Junior Member
     
    #5

    Mar 9, 2008, 06:58 PM
    This weekend I completed the installation of my new Marathon water heater and connection to my geothermal desuperheater. The MR85245 B unit is assume. After bleeding off all the air in the tank, I turned on the power. There was hot water in less then an hour. The desuperheater works better then I expected, water in temperature 90° and out of the desuperheater 165° F. So far I would recommend the Marathon line of water heaters. The insulation of this tank is amazing. The only place you can feel any warmth of the water in the Marathon tank is the outlet nipple. Two thumbs up!

    Eric D
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #6

    Mar 9, 2008, 07:36 PM
    Glad to hear it! Nice system this marathon heater... think we will be hearing about it a lot more. Watch for the need to add that expansion tank... you never know.. ;)

    And thanks for popping in to answer that pump question... I am still waiting for the answer to your question and HKSTROUDs. Just hope he comes back for answers! Good night... Mark
    Eric D's Avatar
    Eric D Posts: 98, Reputation: 4
    Junior Member
     
    #7

    Mar 10, 2008, 03:31 AM
    Mark,

    Like you I was a little concern if I would need a dedicated water heater expansion tank or not with this 85 gallon unit and the desuperheater system. I've been monitoring pressures and temperatures. Late yesterday evening the desuperheater circuit shut its circulating pump down once the inlet side got to 140° F and the pressures all look fine. What I still need to figure out is if I need to lower the set temperature of the lower water heater element. I've been told it is normal to reduce its set point with the desuperheater. I wish there was a simple indicator light at each heating element that would tell if they are on or not. I'm going to call Marathon today and see what they suggest on the set points.

    Thanks again for your input!

    Eric D

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Need help deciding between a tank or tankless water heater [ 19 Answers ]

Which one saves me money; the tankless water heater or conventional tank water heater? :confused:

Surging water pressure & leaking water heater relief valve [ 19 Answers ]

Just recently the pressure of our water in the house surges when we turn a faucet on, and the city water company verified that our pressure in the house when we open a faucet is higher than the pressure in the lines in the street, and after the water runs is at a normal pressure (meaning their...

Connecting a tankless water heater and separate hot water heater [ 6 Answers ]

What I have is this. An oil fired boiler that generates hot water for my house baseboard heating system. Contained within the boiler is a tankless heater that is heated by way of the firebox in the boiler. The tankless heater is used only for domestic hot water. It has a separate CW supply to the...

Hot tub circulation and heating [ 1 Answers ]

I have a tiger river spa bengal model m was here when I bought the house. When just the circulation pump is running the temp stays at where you want it to stay... when you turn the main jets on about 10 min the water cools off... and doesn't warm back up you have to hit the heater thermal cut off...

Hot water re- circulation not working [ 6 Answers ]

I had a loop added from the end of my hot water plumbing to the drain valve on my water heater many years ago. The system has worked great and I found I didn't need to use the pump to get the hot water to flow as gravity did the trick. I just had a new hot water heater installed and now the...


View more questions Search