    Thermostat that goes blank
    We got Honeywell thermostat that goes blank, digital screen, while the heat is on. If we want to increase or decrease the level we have to push button several times and wait until the display comes on and then we can change the setting.
    Is the thermostat bad? Why it would go blank?
    :confused:
    wmproop's Avatar
    wmproop Posts: 3,749, Reputation: 91
    Ultra Member
     
    #2

    Mar 7, 2008, 07:59 AM
    Does it have a battery in it in need of changing?
    gpeck's Avatar
    gpeck Posts: 14, Reputation: 1
    New Member
     
    #3

    Mar 7, 2008, 11:13 AM
    No batteries. It seems it goes blank whenever is set to 67F. At other settings is fine.
    wmproop's Avatar
    wmproop Posts: 3,749, Reputation: 91
    Ultra Member
     
    #4

    Mar 7, 2008, 11:27 AM
    Buy a new thermostat,, or avoid setting it on 67 degrees
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #5

    Mar 7, 2008, 02:55 PM
    Some Honeywell thermostats in the past had problems with the display as they got older. Honeywell still makes one of the best thermostats available.
    gpeck's Avatar
    gpeck Posts: 14, Reputation: 1
    New Member
     
    #6

    Mar 7, 2008, 10:35 PM
    It is a good thermostat, easy to maintain and so far worked for the last 9 years. Summer is coming up and so we'll be using different settings. We'll see how that works.
    Thanks, George
    T-Top's Avatar
    T-Top Posts: 1,871, Reputation: 100
    Ultra Member
     
    #7

    Mar 8, 2008, 06:59 PM
    If a limit switch opens up on the system it will kill 24volts going to the thermostat. A main limit will open because of high temps inside the unit and then reset after it cools back down. Some reasons for the main limit tripping--- dirty filter,dirty evaporator coil,supply vents shut off or restricted,blower set on to low of a speed or blower wheel dirty.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Programmable thermostat went blank [ 12 Answers ]

Our thermostat (which has been serving solely as a thermometer since the last time we used the heat in the spring) blanked out yesterday afternoon. I checked the inside temp. during the day, then last evening the face was completely blank. It is completely unresponsive to any button pushing. I...

Thermostat went blank! [ 4 Answers ]

OK, a summary, Goodman/janitrol heat pump has been working well for 4 yrs. A couple of days ago, the thermostat went blank, with no power to the condenser or evaporator (no I haven't checked voltage yet). I assumed (sorry:() that it was the transformer, so replaced that. No avail. Still no...

Honeywell Blank Thermostat [ 2 Answers ]

I have a Honeywell T8011R thermostat. It is blank. I have 120 vac coming in, the transformer has 28 vac coming out. The 5 amp fuse is fine and the control switch is on. On the circuit board with the 5 amp fuse, the brown wire from the transformer shows 28 vac, the double brown wire under it is...

Thermostat display is blank [ 6 Answers ]

I have a Honeywell programmable thermostat and the display is blank. We had a bad storm and the power went out. I have checked the breaker and reset it. The blower will come on when I switch it to ON, but nothing else works. Can someone help?

Blank Thermostat [ 6 Answers ]

Hi Guys, I had the A/C unit running fine today... then all of a sudden my thermostat went blank... It was raining on and off today here in Plano, Texas... It is a Carrier A/C furnace unit, controlled by a Honeywell Thermostat... This thermostat gets its power from the unit itself... In the...


View more questions Search