    Romex in cold air return
    Is it generally code compliant to run romex wiring through a cold air return duct?
    biggsie's Avatar
    biggsie Posts: 1,267, Reputation: 125
    Ultra Member
     
    #2

    Mar 5, 2008, 08:06 AM
    In many houses the floor joists are used as part of return --- they

    Work well as return ducting -- the wiring should not present a problem...

    I am old school so I guess there may be city codes -- give them a call
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Mar 5, 2008, 02:15 PM
    It is a violation to run NM cable along a space used for environmental air. Crossing one perpendicular to it is fine.
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #4

    Mar 5, 2008, 03:26 PM
    What Stanfortyman said! :)

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Cold air return [ 10 Answers ]

Hello, Is it OK to have a cold air return at the upper wall location vs. near the floor? I just had an old furnace taken out of the main floor and I had one installed in the basement. The installers put the cold air return up on the main floor in a duct located up high piping directly...

Cold air return [ 2 Answers ]

I have a newer house that is about 5 Yrs old. The second floor is always a little cooler than the first floor in the winter and hotter in the summer. The master bedroom and bath are always colder or warmer than the rest of the second floor and even more than the first floor. I have tried to...

Cold Air Return [ 2 Answers ]

Good Morning. I have just finished the divisions and gyprock in my basement and I figure I'm going to have some problems since the only cold air return duct I have down there is in my son's bedroom. Right now I have 2 12X16 bedrooms, a 10X11 full bathroom/laundry room, and about an 18X20 open...

Cold Air return [ 1 Answers ]

My furnace has an adjustable louvered vent on the cold air return. All of the rooms have cold air return also. My question is: Should the louver on the furnace be open or closed in the winter? Thanks, Jon

Romex through cold air return? [ 3 Answers ]

Is it allowable to pull romex from attic (second floor ceiling light) to the basement through the cold air return?


View more questions Search