    Combustion fan keeps cycling after shutdown
    I have a HEIL gas furnace model #NCC5075BHB2. The combustion fan (exhaust blower) cycles on and off for about 20 times after a heating cycle. I have checked, roll out switches, and limit switches; all are closed (have continuity), the pressure switch is open and closes with vacuum. If the pressure switch is jumped or a continuity tester is on it everything works correct. If any sensors are disconnected fan runs constantly. The combustion area is not hot. The only thing I have not checked is the main control board. I would appreciate any ideas on possible fixes. Thanks
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Mar 1, 2008, 08:43 PM
    Sounds like the pressure switch is still making contact all the time or it could be getting a back feed. Check the ground wires from the main panel to the switch for the furnace then to the furnace itself. I am not talking about the white neutral wire but the bare copper or green wire.

    Circuit boards are very sensitive to a bad grounding condition. I have seen a bad ground cause strange things in a furnace and other items.
    Mike_ Butler's Avatar
    Mike_ Butler Posts: 3, Reputation: 1
    New Member
     
    #3

    Mar 2, 2008, 03:18 PM
    Thanks for the quick response. I checked the ground wires all the way to the main electrical panel and also cleaned every other connection I could find in the furnace. I still have the problem cycling on 5 sec and off 3sec. Something is starting the blower and then as soon as the pressure switch senses the change it shuts down which causes the switch to open and the cycle goes on and on. One thing that has me baffled is I have been shutting off the heater with the thermostat switch to keep it from cycling, and it finishes its 5 sec cycle and doesn't come on again. The thermostat should be nothing but an on/off switch based on temperature so if it isn't calling for heat it should be the same as being in the off position. Is it possible the thermostat is somehow causing feed back to the exhaust blower circuit? Thanks for your help; if you have any other ideas please let me know.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Mar 2, 2008, 07:56 PM
    The way to check this is to eliminate the thermostat. Remove the heat wires and all should stop if it is a thermostat problem.
    Mike_ Butler's Avatar
    Mike_ Butler Posts: 3, Reputation: 1
    New Member
     
    #5

    Mar 3, 2008, 05:54 PM
    I replaced the thermostat today and everything seems to be working properly. Thanks again for the help.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #6

    Mar 3, 2008, 06:07 PM
    Glad it worked out for you.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Combustion? [ 2 Answers ]

Hi! I just made an experiment today. We had some liquids (Acid, bases, alcohols) and some solids (metals, salts) and we had to mix them, in order to find some gas-forming reactions. After finding them, we had the write the balanced equations and analyze the reaction. We could also burn the...

Furnace fan cycling switch [ 1 Answers ]

What are the settings about on my gas furnace fan cycling switch.

Fan Keeps Cycling [ 1 Answers ]

I have a Carrier central A/C and a Propane FAG furnace in my basement. The problem is that after the A/C or furnace has shut off, the fans continue to cycle off and on just as if the A/C or furnace was still running.:mad: Sometimes the fans (there is 2 of them, I believe) run continuously and...


View more questions Search