    Determinng the number of lightbulbs that can be used on a circtuit
    Could someone tell me how many light fixtures that would contain 60watt bulbs can safely be placed on one 20amp circuit.
    Thank you.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jan 28, 2006, 10:00 AM
    A 20 Amp circuit 120 volt must be derated 80 %, which is 16 amps. Wattage is calculated by multipling voltage times amperage.

    Ohms Law P = Power or Wattage
    P=EI
    P=120 Volts * 16 Amps
    P=1920 Watts

    1920 Watts / 60 Watts per lamp = 32-60 Watt lamps per 20 Amp circuit.

    Any switches or other devices on this circuit must be rated 20 Amps at minimum of 120 Volt.
    Thad's Avatar
    Thad Posts: 20, Reputation: 2
    New Member
     
    #3

    Jan 29, 2006, 09:48 PM
    Thanks tkrussell, that is easy enough. Thad
    patcolamp's Avatar
    patcolamp Posts: 16, Reputation: 1
    New Member
     
    #4

    Feb 18, 2009, 07:32 PM
    Thad

    When determining how many watts of electricity that you can use on a circuit, the easiest way to do calculate it without all the electrican formulas is to divide the watts used by the input voltage. Example

    60 watts / 120v = .5 or 1/2 amp

    For breaker deration load is 80% of your breaker load. On a 20 amp breaker you should max it out at 16 amps.

    So for 1/2 amp per 60 watt lightbulb. Using a max of 16 amps, you can safely put 32 lightbulbs.

    I hope this helps you out.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #5

    Feb 18, 2009, 07:46 PM
    Quote Originally Posted by patcolamp View Post

    For breaker deration load is 80% of your breaker load. On a 20 amp breaker you should max it out at 16 amps.
    Just so you know. The 80% rule does NOT apply across the board. Sure, it is required for certain installations, such as for continuous loads or electric heat, but not for general use circuits.
    It DOES apply to individual cord and plug connected loads.

    A 20A circuit CAN be loaded to 20 amps.
    See NEC table 210.24

    Also, this thread is THREE(!) years old, and Thad has not been on the site for a year and a half.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

How to get CAF number for POA? [ 10 Answers ]

I had filed 2 tax returns for my friends. They received their Refund check. How can I get CAF number for form 2848? When I filed the returns I entered NONE in the space. Any advice will be helpful. Thank you

How do you change lightbulbs on an enclosed ceiling fixture? [ 2 Answers ]

This one's Hampton Bay and the electrical people took the instructions with them when they left months ago. I don't know how to get the outer ring, which is plastic, off the glass part so I can change the lightbulbs. Do I pry it off with a screwdriver or does it screw off? I've tried to do the...

Number sequence [ 2 Answers ]

What are the next three rows in the sequence: 1 11 21 1211 111221 312211 13112221

1099 tax ID number [ 1 Answers ]

I can't think of the form but there is a form that businesses use to have independent contractors and business that do work with to to fill out. It gives their legal name, contact person, full legal mailing address and either a tax ID number or a social security number Sorry I can't think of the...

AOL 800 number [ 2 Answers ]

? I need a 800 number so I can call American Online - I can't seem to find one - Has anyone have it ?


View more questions Search