    Can Light Junction connection limit
    I am installing canlights in the basement and need a clarification on how many wires I can have in the junction box. It states max 8 no. 12 wire 4 in 4 out through branch circuit conductors. I am using no 12 does this mean I can have a total of 8 wires in the box. I am using it to run to a couple outlets "easier layout" and there are 3 connectors to conduit then a total of 8 wires. The fill calculations seems like it is to many wires but the 8 total has me confused. I can reduce by 1 since the lights and outlets will be on the same breaker. This is just a large open room that will not require arc fault either. Thanks
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Feb 28, 2008, 06:23 PM
    Your post is a bit confusing, but I think I get what you are asking.

    You can use the J-boxes for pretty much anything. It does not matter at all that you are mixing receptacles and lighting.

    The "Max 8 #12" means just that. EACH insulated wire, hot or neutral, counts as ONE. ALL the grounds together count as one.
    So... three 12/2's would be seven conductors; the max you can put in those boxes.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #3

    Feb 29, 2008, 06:35 AM
    I would avoid junction box if possible, and wire from fixture to fixture(daisey chain). Eleminates a lot of problems. May use more wire.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Junction Boxes [ 2 Answers ]

Can I connect a "constant" power source to a "switch controlled" power source in the same junction box? I am putting power to the deck at the rear of my house. One line ( "switch controlled " ) is for the lights, and the " constant power ", is for a GFI, as I don't want to have the GFI tied...

Changing USB connection to ethernet connection [ 1 Answers ]

Hi, I have a belkin wireless G router which doesn't work with my ntl broadband it got something to do with changing the USB connetion to ethernet can someone tell me how Please! Thank you

Making a new connection for ceiling light [ 1 Answers ]

Hi , I just moved into a new house. I am trying to put a light on the ceiling of my basement closet. There is a light bulb 3 feet away from the room. I guess my question is can I or how should I put a new plate in the closet using the light fixture outside? Thanks.

Open limit switch indicator light [ 1 Answers ]

I have a goodman furnace and just the other night I noticed the house wasn't heating, I checked the furnace and the indicator light suggested vent blockage checked the vent stack that leads to chimney and found 2 dead birds in stack removed them and started furnace, thought I had it fixed. All...

Limit switch connection [ 1 Answers ]

I have a Dornbach furnace that has a honewell fan limit switch. I replaced the insert and had to un hook the wires going to the blower fan. The wires on the switch is red black and blue. I never un hooked the blue so it is OK. I also never un hooked the red at the front of the furnace. I have white...


View more questions Search