Ask Experts Questions for FREE Help !
Ask
    DAVIDVESSELS's Avatar
    DAVIDVESSELS Posts: 2, Reputation: 1
    New Member
     
    #1

    Feb 25, 2008, 06:24 PM
    Heat pump
    What happens if you run your heat pump @ 60 degree indoor temp?
    acetc's Avatar
    acetc Posts: 1,004, Reputation: 79
    Ultra Member
     
    #2

    Feb 25, 2008, 07:16 PM
    If you run it in heat it is no problem, if you run it in cool then it may ice up the evaporator coil.
    DAVIDVESSELS's Avatar
    DAVIDVESSELS Posts: 2, Reputation: 1
    New Member
     
    #3

    Feb 26, 2008, 12:01 PM
    Quote Originally Posted by acetc
    if you run it in heat it is no problem, if you run it in cool then it may ice up the evaporator coil.
    Would it not be like running an a/c uint in a low ambiant condition?
    oldmaninthewoods's Avatar
    oldmaninthewoods Posts: 6, Reputation: 1
    New Member
     
    #4

    Feb 26, 2008, 12:13 PM
    I don't understand
    What happens when its 100 degrees outside?
    So I too have a question then
    I am not hvac engineer but I need some help
    Is it possible to put a full heatpump system in an attic
    Both ac and heat with proper attic ventilation and proper downdraft extensions and drainage protection?
    What I missing, the physics?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #5

    Feb 26, 2008, 12:38 PM
    ((would it not be like running an a/c unit in a low ambient condition?))

    You need a special fan control to slow the outside fan down if you are going to run A/C in cool temperatures. That helps to keep up the system pressures so the inside evaporator does not ice up. You also need other items like a crankcase heater for the compressor oil.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #6

    Feb 26, 2008, 01:02 PM
    ((is it possible to put a full heatpump system in an attic
    Both ac and heat with proper attic ventilation and proper downdraft extensions and drainage protection?
    What I missing, the physics?))

    Nothing is impossible but some things are just stupid.
    There is no logic thinking behind that idea.
    Service would be a real pain since changing a compressor requires the use of a torch in the house located in the attic.
    The required air changes would cause the entire ends of the roof to be left off.
    You would also have to figure in lots of head room or you would have a air recirculation problem let alone trying to change a condenser fan motor.
    oldmaninthewoods's Avatar
    oldmaninthewoods Posts: 6, Reputation: 1
    New Member
     
    #7

    Feb 26, 2008, 07:11 PM
    Quote Originally Posted by hvac1000
    ((is it possible to put a full heatpump system in an attic
    both ac and heat with proper attic ventilation and proper downdraft extensions and drainage protection?
    what I missing, the physics?))

    Nothing is impossible but some things are just stupid.
    There is no logic thinking behind that idea.
    Service would be a real pain since changing a compressor requires the use of a torch in the house located in the attic.
    The required air changes would cause the entire ends of the roof to be left off.
    You would also have to figure in lots of head room or you would have a air recirculation problem let alone trying to change a condenser fan motor.
    Stupid is as stupid does
    I have a 8 foot roof over head in this attic
    I could play basketball in it
    That being said I can run metal ducking and cover the entire house from this position
    My concern is the AMBIENT temp in the summer, proper drainage and it would set in a metal pan (special made)
    Why does the ac/heatpump need to be outside?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #8

    Feb 26, 2008, 07:23 PM
    Follow the manufactures instructions. Call the manufacturer to find out if there warranty will cover such install.
    Check with your insurance company and as the if any damage caused by your system will be covered by a attic install of the condensing unit.

    Since your duct will not be in a conditioned space no matter how well you insulate you will have loss and increased utility cost.

    Personally I couldn't care less where you put your system but my experience with commercial hidden equipment built in shopping centers so as not to cause a nasty looking roof line was a disaster. Both from a service point and longevity.

    One last item for you to look into. Go out a watch a heat pump go into defrost. Wait till the end of the defrost cycle and watch what happens when it comes back on line. Under most circumstances water will fly all over the place since for a short time till the coils are dry. I do not believe you would want all that moisture laden vapor all over your insulation/attic space.

    As I said before stupid is as stupid does.
    acetc's Avatar
    acetc Posts: 1,004, Reputation: 79
    Ultra Member
     
    #9

    Feb 27, 2008, 06:28 PM
    To Oldmaninthewoods, I have worked on package heat pumps installed in the attic of a residence such as you describe, the problems that are encountered are not worth the effort, the attics get much hotter then the outside ambient conditions in summer, the air can be ducted to the condenser but the outdoor fan is not designed to move air against a static pressure of ducted discharge air through the roof. The condenser would be hard to clean, noise might be a problem, future replacement would have need to be considered,
    Most codes require an access large enough to replace the equipment.
    The conventional split heat pump system with a outdoor unit on the roof or ground makes most of these problems go away, good luck ,Mike
    oldmaninthewoods's Avatar
    oldmaninthewoods Posts: 6, Reputation: 1
    New Member
     
    #10

    Feb 28, 2008, 10:37 AM
    Thanks mike
    I will consider the split system as I learn more
    You reply is greatly appreciated
    oldmaninthewoods's Avatar
    oldmaninthewoods Posts: 6, Reputation: 1
    New Member
     
    #11

    Mar 2, 2008, 06:42 PM
    Can anyone suggest a good place online to buy a split heat pump system?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #12

    Mar 2, 2008, 07:52 PM
    ((what happens if you run your heat pump @ 60 degree indoor temp?)0

    It just runs and maintains 60 degrees but if you turn the thermostat up and the emergency/resistance heat comes on you electric bill will go way up.
    oldmaninthewoods's Avatar
    oldmaninthewoods Posts: 6, Reputation: 1
    New Member
     
    #13

    Mar 3, 2008, 05:40 AM
    Quote Originally Posted by acetc
    To Oldmaninthewoods, I have worked on package heat pumps installed in the attic of a residence such as you describe, the problems that are encountered are not worth the effort, the attics get much hotter then the outside ambient conditions in summer, the air can be ducted to the condenser but the outdoor fan is not designed to move air against a static pressure of ducted discharge air thru the roof. The condenser would be hard to clean, noise might be a problem, future replacement would have need to be considered,
    most codes require an access large enough to replace the equipment.
    The conventional split heat pump system with a outdoor unit on the roof or ground makes most of these problems go away, good luck ,Mike

    Thanks Mike
    I have asked several (certified) HVAC companies and have gotten MIXED answers

    Question I was quoted a price for LABOR ONLY on the install of 2 unit/ split system
    The quote did not include charging the system or any ELECTRICAL hook-up.
    He would set the units, and run appoximatedly 100 feet total (6 vents) of ducking
    The Round Hose kind and set the vents. And set the return and set the thermostate.
    Most of the labor intensive part of the total system install.

    What price range is acceptable for this type of install?
    What is a fair price for a CHARGE of the system...
    How are the copper lines sold and

    Thanks I am trying to budget this in the next 60 days
    Just don't want ripped off by some fly by night.
    acetc's Avatar
    acetc Posts: 1,004, Reputation: 79
    Ultra Member
     
    #14

    Mar 4, 2008, 06:09 PM
    It appears you got a quote for installing a/c equipment that you would supply, this is not the way to go for your sake. A contractor normally will not provide any warranty on the equipment since he did not sell it to you, get a quote from a licensed contractor (preferably 3 quotes) for a total installation all inclusive, if something does go wrong he can't point a finger at someone else to blame and get a contract in writing.
    I can't comment on price due to labor rates vary from state to state, good luck, Mike
    acetc's Avatar
    acetc Posts: 1,004, Reputation: 79
    Ultra Member
     
    #15

    Mar 4, 2008, 06:11 PM
    As a side note most all air conditioners come precharged.
    oldmaninthewoods's Avatar
    oldmaninthewoods Posts: 6, Reputation: 1
    New Member
     
    #16

    Mar 6, 2008, 06:40 AM
    Thanks for the advice I will check with my local peeps and get 3 quotes

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

NO HEAT! Janitrol heat pump and AC system. Changing to Lux Thermostat. Wiring issue. [ 11 Answers ]

I have a Janitrol A/C and heat pump system. I replaced the thermostat with a Lux T9000LC The A/C works fine, but the heater does not. I have it wired as follows: G - Green Y - Yellow W - White RH - Pink B -

20 yr old Lennox heat pump fan blows constantly in heat mode [ 5 Answers ]

20 year old Lennox heat pump - outside temps been 30's at night, 40's daytime UPDATE: I went outside and the unit is covered in frost on 3 sides! I've been reading on Google about frosted heat pump units and can't determine how to manually defrost it. Apparently, the auto defrost is not...

Why does my air handeling coil freeze up when the heat pump is in heat mode? [ 3 Answers ]

I have a TRANE XL 1200 heat pump. When in the heat mode the air handeling coil freezes up, enough to block the air flow. I can turn the heat pump off and leave the air handeling unit air circulating fan on and get the ice melted. After 30 minutes or so I can turn the heat pump back to the on...

Heat pump thermostat Aux. Light is going on when no resistance heat used. [ 2 Answers ]

I have a Maple Chase SaverStat thermostat on a Lenox heat pump. The thermostat and heat pump are ten years old. Recently when the heat pump comes on the Aux. light on the thermostat also goes on (not the emergency heat light). I have checked and the auxiliary heat strips and they are not heating...

Ductless A/C with Heat Pump - Heat pump does not come on [ 1 Answers ]

Hi The A/C works great but in the morning when its cool outside and I switch on the Heat the indoor unit makes a clicking sound and the fan stays off - after about 8 minutes I switch to A/C I get a rush of ice cold air along with some mist. Seems like when I switch to heat the indoor unit...


View more questions Search