    3 Gang Box, 3 separate circuits
    I have a three gange box with 3 separate 12/2 runs to the panel. There are 3 corresponding 12/2 feeds to the lights.

    My question is, since there are 3 separate circuits, do I need to tie all the grounds together, or only the two that make up that particular light circuit? I would assume whatever I do would also be the same for the neutral?
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #2

    Feb 18, 2008, 08:03 PM
    -All bare grounds need to be tied together
    -The neutrals are treated different. Each circuit neutral should be wirenutted to any neutral related to that circuit. >>>>Not circuit neutral "A" to circuit neutral "B"<<<<<
    -Now you could turn two of the circuits into a multi-circuit, but I'm not going to confuse the situation.
    hardwiredman's Avatar
    hardwiredman Posts: 11, Reputation: 1
    New Member
     
    #3

    Feb 18, 2008, 08:07 PM
    Thanks for the response, I'll tie all the bare grounds together, and leave the hot and neutral's separated for their respective circuit.
    hardwiredman's Avatar
    hardwiredman Posts: 11, Reputation: 1
    New Member
     
    #4

    Feb 18, 2008, 08:08 PM
    I am curious however as to what a multi-circuit would be?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #5

    Feb 18, 2008, 08:32 PM
    A MWBC is a circuit where two hot conductors share one neutral.
    hardwiredman's Avatar
    hardwiredman Posts: 11, Reputation: 1
    New Member
     
    #6

    Feb 18, 2008, 09:03 PM
    Simple enough.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #7

    Feb 19, 2008, 05:56 AM
    Multi circuit will have 2 hots sharing neutral, the 2 circuits must be fed by breakers on opposite phases. Has a cancelling effect. If both circuits drew 20 amps the neutral will draw Zero. If someone unknowingly switched breakers around and both were on same phase, then if both were drawing 20 amps, neutral would be carrying 40 Amps.
    Goosd Luck.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #8

    Feb 19, 2008, 11:58 AM
    Just a comment. It does set the stage for ground loops, but if you pretend that it was done in conduit and you had a metal box, that is what you would get. I don't want to go against code.
    If these circuits contained grounding outlets, I'd be much more concerned about ground loops.

    If CODE WOULD ALLOW, I'd be happier with insulating the grounds and keep them with their respective circuits, like they might be if using a plastic box. Then connect switches to their appropriate ground with a pigtail.

    For the metal box case, do the same, except pigtail only one of the grounds to the box and the various switches. In the metal box case, only one ground handles the exposed stuff on the box and switches.

    If you draw the two diagrams, the way proposed will case loops. My proposals will not..
    But you have to do what CODE says. Can anybody provide a reference?

    Thiis would effectively eliminate ground loops.
    hardwiredman's Avatar
    hardwiredman Posts: 11, Reputation: 1
    New Member
     
    #9

    Feb 19, 2008, 01:55 PM
    It is 3 lighting circuits, plastic box. I spoke with the local inspector and he confirmed that all of the ground will be made up as one, so that's how I'll do it. Thanks everyone for the comments.
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #10

    Feb 19, 2008, 02:10 PM
    U are welcome!

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

5 gang switch box [ 7 Answers ]

I have a 5 gang metal switch box with 5 switches. I want to eliminate one of the switches so I have only 4 switches. I don't want to use a blank to fill the hole with no switch. I want to use a switch plate for 4 switches. Can I cover the hole with a metal plate and mud over it so it looks like a 4...

Wiring new circuits , junction box sizes. [ 11 Answers ]

Hi All, I need some help guidance for a home project. I am installing all new 4 lights and 2 outlets. I have pulled a 12/2 romex (2+ground MAIN ROMEX) from the main panel. I using "star" topology versus "daisy-chaining) as circuits are spread out in different locations. By using star topology one...

Timer switch in triple gang box OK? [ 7 Answers ]

Hi - I recently installed a timer switch for my front porch light. It seems to be working fine. However, after installing it I noticed the package said "for use in double gang box." I have it installed in a tripe gang box, along with a conventional light switch, and a three-way light switch. Is...

Is Congress a Gang? [ 1 Answers ]

"Is Congress a gang, and does it need to be abated?" And we not-so-assertively assert that "Sometimes Congress could be a gang, depending on the future use and misuse made of Senate bill 155 -- the Gang Abatement and Prevention Act." And so could your motorcycle club, your chess club, your rose...

SHirt Tales? Get Along Gang? [ 3 Answers ]

Ok, so I grew up in the 80's and there was this cartoon with many different animals that had shirts on, and they would say different words depending on their moods (I think) Was this show called "Shirt Tales" or the "Get Along Gang"? I think the Get Along Gang was a different cartoon with animals...


View more questions Search