    OK.. I am running a line out to my new garage. Its coming out of my 200amp service into a 125 amp sub panel with a 125amp breaker.

    Question is, can I use 2224 for this. And if so can it be buried in conduit? I assume 2224 will carry 125 amp, as my thinking is it is 3 #2 wires (2 Hot,1 Neutral) and 1 #4 for grounding(2224). I assume Ill have to get #6 or 8 to run from the gnd rod back up into the euipment ground buss.

    Also seen some 1113 ser I think that's what it was. Would that work better?

    Does all this make sense? Will 2224 carry this load, can it be used under ground in conduit.. Those are my 2 questions. I think its 2224 AL I was looking at today. Is there a diff in AL and NON Al.? Any help will be appreciated!
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Feb 15, 2008, 07:24 AM
    For a residential 125 amp feeder, neither of the wire sizes you mention are correct.

    This will need a min of #2 copper or #1/0 aluminum.

    You mention 4 wire cable ,which is correct, but need to know what type of insulation the cable has to understand if it can be buried.

    Typical insulation for underground is USE for direct bury, and XHHW for installing in an UG conduit.


    If all you have available is #2 AL, then the feeder can only be 100 amp.

    Exactly what size and type cable are you considering?
    needhelp200's Avatar
    needhelp200 Posts: 2, Reputation: 1
    New Member
     
    #3

    Feb 15, 2008, 03:00 PM
    I see now. So all I need is 1/0 Al Or #2 copper. Gotcha I can handle that. I assume I will need 3 of those the same size for hots and Neutral, then most likely #6-8 for equipment Gnd. And the same for the ground rod I have to drive in at the shop.


    Now I assume that they sell a reducer or something so as to get 1/0 wire into the breaker and ground buss? I have heard of people trimming off some of the outside strands in order to make it fit. Sounds like trouble to me

    Lastly, I noticed in depot that there are regular ground buses AND equipment buses. Is there a difference in the 2. They looked the same to me. But Im not sure.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Feb 16, 2008, 06:25 AM
    For a 125 amp feeder, the equipment ground needs to be a min of #6 copper or a #4 Al.

    Use may use either #8 or # 6 copper to run from the equipment ground bar to the ground rod also.

    Never cut strands off a conductor to make fit in a wire connector.

    A panel or breaker rated 125 amp should allow #1/0 to fit. Read the data sheet on the terminations, it will list the wire range the connector is rated for.

    There are crimp on wire reducers, but only available at electrical distributors, and required special crimping tools and dies to install properly.

    If something does not allow a larger wire, then a mechanical lug will need to be added.

    I do not know what a "regular" ground bar is. You should find two types, one is a Neutral bar, which will come with insulating mounting feet, and equipment ground bars, which are intended to be bolted directly onto a metal box using machine thread screws.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Confused.a lot [ 8 Answers ]

Well, I'm turning 14, and I'm really confused. It's just everything I hear or see it's all about how when you get older life becomes difficult with a lot of responsabilities, a lot of problems etc. and also it's like I'm afraid of time as because of all this I fear of growing up :( . I also can't...

Confused a lot about this girl [ 66 Answers ]

Hi all, I've read a lot of different posts on here which have been a huge help, but have a scenerio of my own. In short, perfect 2 1/2 year relationship is falling apart because she feels like she has lost herself. Ok, give her more space. Few days later she doesn't know if she wants to be with...

Maybe a little one? [ 4 Answers ]

So I am late on my period and I'm very regural my husband came in me I think the 7th of July and that's when I was fertile I didn't get my period last month I was suppose to get it the 7/27/07 now it's the 10th and nothing yet my boob hurt and my vains are showing more and I'm bloated but I'm not...

Lot of questions... confused... please help [ 3 Answers ]

Hello, I arrived in the US in Aug 2001, been on F-1 until September 2005. Got my H-1 on Oct 1st 2005. Joined Company A in May 2005 but their pay roll deducted my ssn and medicare taxes not considering my status. Changed to company B in Dec 2005. My questions are: 1)I am a non-resident...

The little kittey is confused [ 1 Answers ]

If anyone gets this, mail me back so i know this works because i am soo confused on how to do this! Kat!


View more questions Search