    How to install/connect 2nd ground rod for 2 boxes
    I have been told I need second grounding rod. I am on well with plastic external pipes, however inside the house is copper. I have two boxes and one ground pole.The second box is grounded to the other box. I am trying to correct electrical shock in basement shower.
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #2

    Feb 6, 2008, 08:35 AM
    A 10 " driven ground rod is acceptable in many situations but we don'where you live or what your water table is like. Have you looked into what is causing the short?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Feb 6, 2008, 08:44 AM
    All you need to do is drive another ground rod, no closer than six foot away from the existing rod, and connect with a copper wire sized accordingly to your service, and connect with a ground rod clamp at both rods.

    Now that I explained that, why do you think that this is going to solve your problem with shocks in the shower?

    I doubt that this will help at all.

    How is the second box grounded to the first?

    Is the inside copper water line bonded to the service? How?

    Exactly where are the shocks being felt?

    Any idea what the voltage is at this shock point?


    You can drive and connect the second rod, and see where that gets you, and get back with more details as I am sure you will have more questions how to solve this problem.
    Jackson6112's Avatar
    Jackson6112 Posts: 8, Reputation: 1
    New Member
     
    #4

    Feb 6, 2008, 04:10 PM
    Krussell; The voltage flucuates up to 12 volts. The second box is grounded with copper strain wire. The copper pipes are grounded to box with strain wire. The ground is also done with strain wire to the pole. The shower is in basement. Also get shock from outside faucet when ground is wet.
    Jackson6112's Avatar
    Jackson6112 Posts: 8, Reputation: 1
    New Member
     
    #5

    Feb 6, 2008, 04:20 PM
    tkrussell;

    I have been told by master electrican that wiring in house is OK. He believes there is nuetral problem in ground. Power company does not agree. They do both agree that it needs second ground pole for second box. Also, water is from well with plastic pipe outside house and copper pipe inside. Drain in shower is pvc. Get shock when water is running in shower and touching faucet and when ground is wet from outside faucet.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #6

    Feb 6, 2008, 04:53 PM
    There is a serious issue with the neutral and ground. There are many possibilities, mostly caused by a loose connection, or more, at any one of a dozen or so connections.

    And the grounding may not be proper, but adding a ground rod is not the sole solution.

    The electrician should know how to troubleshoot the utility neutral, and review the entire grounding system for any defects.

    If not, look for a good quality service electrician, one with the proper troubleshooting skills and instruments.

    Without pictures, I doubt you can explain the extreme detail needed to help us point to any specific problems.

    Sure sounds like a utility problem if the electrician checked the home.

    Did anyone open the meter socket? That usually gets missed.
    Jackson6112's Avatar
    Jackson6112 Posts: 8, Reputation: 1
    New Member
     
    #7

    Feb 6, 2008, 06:33 PM
    Tk russell;A picture of what would help? The 2 open boxes?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #8

    Feb 7, 2008, 10:57 AM
    Yes, pictures will help us see what you have, open panels, grounding clamps or locations, at least a pic of the meter. Anything will help, as there are too many what ifs to go over, easier to see what you have and we can go from there, hopefully.
    Jackson6112's Avatar
    Jackson6112 Posts: 8, Reputation: 1
    New Member
     
    #9

    Feb 17, 2008, 04:14 PM
    TkRussell;

    Sorry it took so long to send picture. Thanks for your help.
    Attached Images
     
    EPMiller's Avatar
    EPMiller Posts: 624, Reputation: 37
    Senior Member
     
    #10

    Feb 18, 2008, 01:53 PM
    Jackson,

    Are both boxes fed from one meter? Is the water line bonded into the same panel as the ground line to the ground stake or is it in the other panel? Or is the ground stake connected out at the meter base only?

    Are you familiar with working on ground wiring? There may be little or no voltage present but there can be enough current to kill you. Don't open any connections on ground wires without ADEQUATELY bypassing them first. And don't do this if you don't understand what I said.

    Do you have a good DMM and are you comfortable testing around live equipment? I can give you a couple of tests to try, but I need to have answers to the other questions first.
    Jackson6112's Avatar
    Jackson6112 Posts: 8, Reputation: 1
    New Member
     
    #11

    Feb 18, 2008, 06:26 PM
    EPMiller;
    Both boxes are fed from one meter. Water is bonded into the left box and the ground stake is from the right box. I do not know what you mean by bypassing. I am comfortable testing live equipment. I have average DMM.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #12

    Feb 18, 2008, 08:19 PM
    Quote Originally Posted by Jackson6112
    Water is bonded into the left box and the ground stake is from the right box.
    EACH service enclosure must be bonded to the water piping and also to a grounding electrode. The way yours is set up is not right.

    Several NEC sections apply here: 250.58 is a main one. Many parts of Art. 250 II & III actually apply.

    Are both main bonding jumpers installed (screw or strap bonding the neutral to the panel box)?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #13

    Feb 18, 2008, 08:27 PM
    This graphic will give you an idea, although the notes do not apply here:

    ® Mike Holt
    EPMiller's Avatar
    EPMiller Posts: 624, Reputation: 37
    Senior Member
     
    #14

    Feb 19, 2008, 06:46 AM
    Quote Originally Posted by Jackson6112
    ... I do not know what you mean by bypassing. ... I have average DMM.
    Jackson,

    By 'bypassing' I mean establishing another alternate ground that will serve to keep the system grounded when you open up a connection that you see as questionable. You should NEVER break the grounding conductor or connections on a live system.

    As to your DMM, what you need is one that will reliably read low VAC. What you should do is look closely at every connection in the grounding wiring and if you see anything suspicious, set the DMM to a low voltage AC range (400mV is nice if you have it) and check if there is any voltage across that connection. If there is an actual reading, not just the meter settling, then there is resistance there that is raising the impedance of the grounding system which will show up as voltage on the ground buss. Another thing I have done already is extend one of the leads of my DMM out to the ground stake and checked the resistance from the panel ground buss. Of course you have to take the added lead length into account. Check your meter reading with the long lead before you do that test setup. All this assumes that you are careful making good contact with your leads. A DMM is only 9 volts and can't do the job of a megger. You may or may not be able to find your problem with this method.

    The shock that you are getting in the basement shower is the electricity from the mains that is finding an easier path to ground through you than through the electrical service ground system. If as you say the plumbing is grounded in one panel and the ground rod is out of the second panel you have several connections that could cause impedance trouble. Especially look at the connection where the ground system wiring is connected to the house water pipes.

    Late addition: I forgot to say that when you do the voltage check on the ground connections, there must be current flowing in the conductor. You can check that if you have a clamp meter, but if you turn off every other ROW of single pole breakers in the panel you will be drawing current from only one leg of the service. If you turn on a bunch of lights and such, that should get you several amps to do your measurement.
    Jackson6112's Avatar
    Jackson6112 Posts: 8, Reputation: 1
    New Member
     
    #15

    Feb 19, 2008, 12:48 PM
    Stanfortyman; There are 2 4strain wires going between each neutral/grounding bar in each box. Does this do it?
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #16

    Feb 19, 2008, 01:38 PM
    I do believe groundsin this case have to be a solid conductor. Stranded conductors are not permitted. Can someone confirm that?

    I know that in my house, the water pipes are the grounding electrode. The pipes also pass underground. This was permitted back in the day. An allowed fix was to bond both side of the water meter if the water meter was plastic.
    Jackson6112's Avatar
    Jackson6112 Posts: 8, Reputation: 1
    New Member
     
    #17

    Feb 19, 2008, 02:25 PM
    KeepitSimpleStupid; I have plastic pipes from well to holding tank. From holding tank on are copper.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #18

    Feb 19, 2008, 02:56 PM
    Quote Originally Posted by Jackson6112
    Stanfortyman; There are 2 4strain wires going between each neutral/grounding bar in each box. Does this do it?
    That may fly for some inspectors but I would not do it that way. I guess it performs the same task in the end.

    Can I assume you are referring to stranded wire when you say "4strain"?


    KISS, unless there is a local amendment solid or stranded is fine.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Where to install a Grounding Rod [ 14 Answers ]

My house is about 20 years old and I do not have a grounding rod installed. Although all the wiring is grounded to the water pipes, I would still like to install one. My question is how close or far from the main electrical box should the grounding rod be installed? On on the other side of the...

Sub-Panel Ground, Wire or Rod [ 9 Answers ]

I running a 70 amp sub-panel to a shop that does have telephone connections to the main house. I know that I need to isolate the ground from the neutral at the sub-panel. I am planning on running 3, #4 wires to the sub-panel and I also have an 8' ground rod, which I will connect as well. My...

Ground Rod Installation [ 4 Answers ]

I am installing a concrete patio 20'x18' over the area where the ground rod is currently installed. If I relocate the ground rod, what is the maximun distance from the main panel can the ground rod be installed?

Ground Rod Height? [ 3 Answers ]

Hi, new homeowner... I just recently discovered this technological advance known as a "ground rod!" I apparently have two: one by my house and one by my pool. They stick out about 9 inches above ground level. They're unsightly and begging for someone to trip over them. Can I hammer...

No ground rod at main breaker. [ 10 Answers ]

I have been reading threads here but want to be sure I understand since electricity is potentially so dangerous. I have an old house. My main breaker box below the meter has two large hot legs and an uninsulated neutral. There is no ground terminal. There is no ground rod. I'm sure something is...


View more questions Search