Ask Experts Questions for FREE Help !
Ask
    zephres's Avatar
    zephres Posts: 1, Reputation: 1
    New Member
     
    #1

    Feb 5, 2008, 08:46 PM
    Furnace shut down
    A goodman furnace. Starts up with the induction fan.. and runs good, then electronic ignighter glows and the gas valve opens , then gas lights and system runs for about 10 seconds, then when the blower kicks on but everything else shuts off except the blower , I thought it was the PC board so I replaced it with no change to operation. I also replaced the flame scensor.. nothing. I then tested startup amps on the blower and got 11amps on start up. I tested the unit in AC cool mode and blower runs fine... with No shut down.. all safety scensors are good and not infuencing the PC board. I have a feeling that the run capacitor and maybe motor too are pulling too much amps (AT LEAST ON STARTUP) in the heating mode and triping the PC somehow.. help
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Feb 5, 2008, 09:30 PM
    I guess that would be possible about the run cap but that would be a very strange thing to happen.

    I would check all the grounds from the electric panel to the furnace disconnect switch and then from the switch to where it attaches into the furnace.

    The furnace needs a good chassis ground for the electronics to function properly. I suggest you loosen up all grounds then retighten them so they are proven tight. While you are in there you might as well check the white neutral and hot legs for tightness also.

    A different person posted he replaced almost all parts on a Goodman and I told him the same thing I am telling you. He posted back that the ground in the furnace disconnect was loose and tightening it up solved the problem.

    He said he felt kind of bad because he spent all that money for new parts and it ended up being a ground. Also check any grounds to the circuit board.
    NorthernHeat's Avatar
    NorthernHeat Posts: 1,455, Reputation: 132
    Ultra Member
     
    #3

    Feb 6, 2008, 05:38 AM
    I would also check to see if the pressure switch is opening shortly aflter the burners ignite. Then you are looking at a venting issue.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Furnace won't shut off [ 2 Answers ]

My electric furnace was kicking the breaker and shutting down. I'd reset and it would work fina a week oe two then blow it again. Now it won't shut down. Is this a thermostat problem or something else.

Furnace will not shut off [ 3 Answers ]

Recently installed a noma programmable thermostat and same worked fine for four days but today the furnace would not shut off despite the temp rising to 78+F. The temp was set for 67F. The only way to get the furnace to stop running was to shut it off manually. How do I correct this problem?

Furnace will not shut off [ 1 Answers ]

I have an electric Coleman furnace which comes on when it should, but will not turn off When the set temp is reached. Even manually using the on/off switch will not stop it. The only way is to flip the circuit breaker. What is going on ? Thank you.:confused:

Furnace will not shut off [ 1 Answers ]

I have a 20+ year old Coleman furnace with AC. The White Rogers thermostat has four wires connected, RC, W, G, Y. There in no jumber from RC to RH. There is a blue wire embeded in the wall but is not connected on either end. The AC worked great in hot weather. The problem now is that when the...