New Member
|
|
Jan 31, 2008, 02:10 PM
|
|
Wiring Honeywell thermostat T8411r to RTH3100C
Hello everyone. If you have an answer or even a suggestion, to my problem please let me know. I have been going crazy trying to figure this out.
I am replacing a bad Honeywell (T8411r) thermostat. The LED lights went out and I could no longer see to adjust the temp. The HVAC unit worked perfectly when I removed the thermostat.
I went to Home Depot and bought the closest thing I could find to the old T8411r... a Honeywell model RTH3100C (it has the identical switch layout). I had no idea at the time what a pain this was going to be to swap out.
The original wiring on the T8411r was as follows:
'Yellow' - Y (and jumped to W1)
'White' - W2
'Green' - G
'Orange' - O
'Red' - R
'Blue' - C
(There are two unused and covered wires... Brown and Black)
The instructions for the new RTH3100C state that I should attach the wiring as follows:
'Yellow' - Y
'White' - AUX
'Green' - G
'Orange' - O
'Red' - R
'Blue' - C
I did this and installed the batteries/faceplate. The 'cool on' message comes on and slowly flashes for about 5 minutes as it is suppose to, but then nothing happens. There is absolutely nothing... no fan, no AC, and no heat. I tried all switch settings and could not get the unit to turn at all. I also tried to switch the AUX (White) and Y (Yellow) wire but to no avail.
If anyone has any suggestions as to what I could try, it would be greatly appreciated. I am at a loss for what to try next.
Thanks !
Gary
Frustrated in Saint Pete -
|
|
 |
Ultra Member
|
|
Jan 31, 2008, 02:29 PM
|
|
Its possible you could have blown the transformer when installing,, did you check with meter to see if you had 24 volts at the red tstat wire?can be checked at the tstat, or at the furnace also double check the breakers to the furnace,, stranger things have happened
|
|
 |
New Member
|
|
Jan 31, 2008, 03:46 PM
|
|
Thanks for your reply... Yes, I am possitive that the transformer is okay. I painstakingly took the time to re-install the orig T-Stat to make sure that the system was still okay. The unit came on so I know all is well with the system.
|
|
 |
Junior Member
|
|
Jan 31, 2008, 05:09 PM
|
|
I'm not fimiliar with this t-stat but from what you've said to me looks like you need to put that jumper back to Y-W1 and make the white wire W2
|
|
 |
Junior Member
|
|
Jan 31, 2008, 05:12 PM
|
|
Sorry that's not right
|
|
 |
Junior Member
|
|
Jan 31, 2008, 05:13 PM
|
|
I don't believe you have a 2 stage heating t-stat wich is what the original is
|
|
 |
New Member
|
|
Jan 31, 2008, 05:24 PM
|
|
I am not exactly sure what 'two-stage' means, but do you have any idea as to how I can change the wiring and get this thing up and running? Thanks.
|
|
 |
Heating & Air Conditioning Expert
|
|
Jan 31, 2008, 08:06 PM
|
|
In the old thermostat wiring
REMOVE JUMPER, WHEN SUPPLIED, FOR SYSTEMS WITH Separate HEATING COMPRESSOR CONTACTOR (W1 SEPARATE FROM Y).
Old thermostat link
http://customer.honeywell.com/techli...0s/69-1037.pdf
New thermostat link Note look at page 12
http://customer.honeywell.com/techli.../69-1889EF.pdf
I believe you have a wire or two crossed.
I have supplied you with the manuals for both thermostats. You should now have enough information so that you can wire it up correctly. I am sure you marked which wire came from where on the old thermostat just like it says to do in the manual for the new thermostat. If not then you will have to trace the wires back whence they came and see what part of the unit they operate.
|
|
 |
New Member
|
|
Feb 1, 2008, 12:40 PM
|
|
Thank you very much (HVAC1000) for the valuable information. I will be working to resolve this problem all weekend (if need be) and will report back with the results.
|
|
 |
New Member
|
|
Dec 31, 2009, 03:11 PM
|
|
I am replacing a energy star LUXPRO thermostat with a Honeywell RTH3100C Thermostat. My heating unit comes on and blows cold air for about five minutes and shut off. I jumpered the E and Aux , yellow, green and red are connected properly. The white wire is also connected te aux. Can some one please let me know if I wired the thermostat incorrectly. My 50th bithday is on New Years Day and Friends and family are scheduled to spend time with me. Thanks
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Wiring Honeywell RTH3100C thermostat
[ 2 Answers ]
I replaced my old mechanical thermostat with a Honeywell RTH3100C digital. My heatpump is an older Rheem. My wires are RED,YELLOW,GREEN, WHITE AND WHITE1. I connected the red,green,yellow to their respective terminals. I don't know what to do with the White1. The blower comes on and with the White...
Honeywell T8411R Thermostat Wiring
[ 3 Answers ]
Someone gave me this digital thermostat which was used & has no instruction papers. I have a Goodman Heating & A/C self contained unit outside for a mobile home. The old thermostat was a 4 wire system with a green wire on the G terminal, red wire on the RC terminal, blue wire on the Y terminal, and...
Wires on honeywell thermostat T8411R
[ 2 Answers ]
I was painting my wall and I decided to remove my thermostat off the mounting plate, after I finish I put it back but it didn't work anymore, so I check the wires and noticed a black wire that was loose, all the other wires were in place, so I tried to tight those but a think I accidentally touch...
Replacing Honeywell T8411R with Honeywell RTH7500 - wiring problems
[ 1 Answers ]
I need help getting my new, programmable thermostat to work. I currently have a dual-stage Heat Pump and A/C unit that works fine. The current thermostat is the Honeywell T8411R. I don't know the number for the subbase, but it's the one that came with the thermostat. The current (operational)...
Honeywell thermostat model #t8411r
[ 1 Answers ]
Our system controls both the central air and heat in our home (which is a rental). Yesteday I noticed that after I had switched on the heat that the thermostat was no longer working. We have checked all the breakers and examined the circuit board, however, I am still in a quandry if this is a...
View more questions