    Heat pump has no heat
    I came home and the programmable thermostat says "no ac power". So I check the batteries in the thermostat. Good. Then I check the breakers. Good. Then I check the outside unit. Obviously nothing is going on but I did hit the main contactor and the unit came on. I thought that was interesting. I tried to check the fuses outside, but I'm like the unit would not have come on if they were bad. I'm just wondering if the thermostat is bad. I need help quick!
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Jan 30, 2008, 11:50 PM
    Usually a no ac signal means that no power is being supplied to the thermost from the inside air handler/furnace.

    Check fuses/circuit breakers for the inside unit.
    Check the 24 volt transformer that is in the inside unit for 24 volts output.

    Report back after testing.
    snoopy74's Avatar
    snoopy74 Posts: 2, Reputation: 1
    New Member
     
    #3

    Jan 31, 2008, 06:20 AM
    Quote Originally Posted by hvac1000
    Usually a no ac signal means that no power is being supplied to the thermost from the inside air handler/furnace.

    Check fuses/circuit breakers for the inside unit.
    Check the 24 volt transformer that is in the inside unit for 24 volts output.

    Report back after testing.
    Ok so I checked the transformer and I got 20v instead of the 24v I expected. I checked the red and white wires coming from the transformer. I checked them at the thermostat and I got .8 volts.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Jan 31, 2008, 07:06 AM
    You have a defective wire somewhere not allowing the voltage to pass to the thermostat.
    OR it is possible a fuse blew on the circuit board.

    OR there is a device like a limit control or another control in the inside unit to not allow the 24 volts to pass to the thermostat.

    That seems like a lot of places to check but I am just trying to give you as many options as I can think of.

    BTW 20 volts could be OK since I do not know how accurate your meter is.
    You might remove all the wiring on one side of the transformer and retest. It could have a small load on it that would drop the voltage.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

NO HEAT! Janitrol heat pump and AC system. Changing to Lux Thermostat. Wiring issue. [ 11 Answers ]

I have a Janitrol A/C and heat pump system. I replaced the thermostat with a Lux T9000LC The A/C works fine, but the heater does not. I have it wired as follows: G - Green Y - Yellow W - White RH - Pink B -

Heat Pump blower, and heat, won't turn off- not contr. Bd. [ 0 Answers ]

I've read about blowers (heat pump) that won't shut off, no matter what done to thermostat, and the cause typically being a faulty control board, and/or fan relay on contl. Board. I replaced board, as tech removed green wire to demonstrate it's fault (didn't turn blower off), but tried a brand new...

20 yr old Lennox heat pump fan blows constantly in heat mode [ 5 Answers ]

20 year old Lennox heat pump - outside temps been 30's at night, 40's daytime UPDATE: I went outside and the unit is covered in frost on 3 sides! I've been reading on Google about frosted heat pump units and can't determine how to manually defrost it. Apparently, the auto defrost is not...

Why does my air handeling coil freeze up when the heat pump is in heat mode? [ 3 Answers ]

I have a TRANE XL 1200 heat pump. When in the heat mode the air handeling coil freezes up, enough to block the air flow. I can turn the heat pump off and leave the air handeling unit air circulating fan on and get the ice melted. After 30 minutes or so I can turn the heat pump back to the on...

Heat pump thermostat Aux. Light is going on when no resistance heat used. [ 2 Answers ]

I have a Maple Chase SaverStat thermostat on a Lenox heat pump. The thermostat and heat pump are ten years old. Recently when the heat pump comes on the Aux. light on the thermostat also goes on (not the emergency heat light). I have checked and the auxiliary heat strips and they are not heating...


View more questions Search