    GFCI delayed tripping
    Installed new GFCI receptacle in bathroom. Tested allciecuits on line with GFCI tester and all indicate OK. After exactly 3 minutes the GFCI trips. This was repeated several times. Replaced the GFCI receptacle with a new one and same results.:confused:
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jan 28, 2008, 05:44 AM
    Do you have something connected to the Load side terminals of the GFI?

    If so, there may be a ground fault on the circuit downstream of the GFI device.

    If not, be sure the Line feed connects to the LIne terminals of the GFI.

    Get back with more detail.
    philip912's Avatar
    philip912 Posts: 3, Reputation: 1
    New Member
     
    #3

    Jan 28, 2008, 10:36 AM
    When disconnected from the gfci the line side is hot and the load side is dead. Line side is connected to line side of the gfci and the load is connected to the load side. Everything on the load side is disconnected. When the gfci is reset it trips exactly at 3 minutes. 5 receptacles on the load side were replaced with new Leviton receptacles and tested with gfci tester and all test OK. This tripping was repeated 5 times at exactly 3 minutes.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #4

    Jan 28, 2008, 12:50 PM
    Does it trip in 3 minutes when the load is disconnected?? If so
    Remove GFI from wall, disconnect ground so only hot and neutral are connected to GFI, See if it trips in 3 Minutes.
    philip912's Avatar
    philip912 Posts: 3, Reputation: 1
    New Member
     
    #5

    Jan 28, 2008, 12:56 PM
    I'll give it a try!

    Thanks for the quick reply.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

GFCI Breaker Tripping on Coast Spa [ 4 Answers ]

Hi, I am having a problem with my Coast Platinum Series Spa bought in 2001. The GFIC breaker is tripping. Spa information: Coast Platinum Series Model – ML40 Serial number – 004629 Control Pack/Circuit Board - TSPA-1-P122-P222-B1-01-CP1-H34.5-JJM-FL-RL-CC23453-01C Two Monster Flow 7.0...

GE Refrigerator keeps tripping the GFCI switch when plug in. [ 2 Answers ]

I cleaned my refrigerator and shortly afterwards it trips the GFCI outlet every time its plugged in. Did I blow a fuse inside the refrigerator or short circuit something out. If there is a fuse where is it usually located. Thanks for any help!

Gfci spa panel tripping [ 4 Answers ]

I just installed a spa with 4 wires. The house is old and while the neutral & ground bus bars are separate in the spa panel, they are all on the same bar in the main panel. Do I need to install a ground rod by the spa panel to keep the gfci from tripping? (instead of running the ground back to the...

Pond pump tripping GFCI [ 1 Answers ]

Three years ago a new outdoor GFCI outlet was installed mainly to run a small pond pump. I mean small.. the pump is about the size of a baseball, but keeps the pond water circulating well enough. Just within the past two weeks, the outlet kept tripping, I quickly determined it must be the pump(left...

False Tripping GFCI and SPAS [ 1 Answers ]

I have a 240volt spa, and I hooked the electricity myself. I installed a 70 AMP breaker at the main panel and purchased a spa panel from Lowe's. The panel includes a GFCI 50AMP breaker and includes extra places for lighting and what not. My spa requires 4 wires (2 hots, neutral, and ground)....


View more questions Search