Will this work for basement bathroom venting?
I'm planning a basement bathroom where the plumbing was stubbed in during construction. The plumber installed a 2" pipe for a sink, 2" w/trap for a shower and 4" for a toilet. I would like to move the sink from the original location. I chiseled up the concrete and capped the sink line that was already stubbed in. I would like to move the sink to the other side of the room and tap directly into the main 4" stack.
Please see the attached picture which shows the old and new sink location. There are no vents installed yet. I'm guessing the plumber planned to vent the sink which I think would vent all three fixtures. Can I move the sink to the new location and vent it with an air admittance valve under the vanity? Would this take care of the venting requirements for all three fixtures? Is there any particular importance to sink (and vent) being upstream from the other fixtures in the original plan and downstream in the revised layout?
By the way, this new layout lets me install a 60" tub and 60" vanity where the old would have required a corner shower and 24" vanity.
|
|
 |
New Member
|
|
Jan 19, 2008, 06:58 AM
|
|
Another thing to add is that the old sink location is probably at the end of the same line as the shower and toilet while the planned new sink location would be to go directly into the main stack.
|
|
 |
Eternal Plumber
|
|
Jan 19, 2008, 09:11 AM
|
|
You may move your lavatory but first you must know what's under the slab and how it's vented. In the old configuration the toilet drain line connected to the main. The lavatory drain line connected to the toilet drain and wet vents the toilet. The shower then connects to the lavatory drain line and is wet vented by it. By capping off the lavatory stub up you have capped off the groups vent.
To make this work you will have to uncap the lavatory stub up and use it as a dry vent for the shower and the toilet. In addition to that you will have to run a separate vent for the new lavatory. These two vents can be tied together and run out the roof, revented back to a roof vent in the attic or, if local codes permit, can be vented by one or two AAV's. Good luck, Tom
|
|
 |
New Member
|
|
Jan 19, 2008, 09:45 AM
|
|
Thanks. That same thought crossed my mind last night when I remembered the old lav drain when up into a T, probably for a vent. Can I simply reconnect the line I capped into a vent and tap the new lav directly into the main stack with a AAV under the vanity?
Pictures below are what I'm looking at. The main stack is 7 feet from the toilet.
|
|
 |
Eternal Plumber
|
|
Jan 19, 2008, 10:39 AM
|
|
Can I simply reconnect the line I capped into a vent and tap the new lav directly into the main stack with a AAV under the vanity
Yes, If the vent you connect to is a dry vent,(no fixtures draining above it) and local codes allow a AAV. Cheers, Tom
|
|
 |
New Member
|
|
Jan 20, 2008, 09:31 AM
|
|
Thanks for your help. I noticed that there is a 1.5" pipe that is Y'd off near the top of the main stack. This pipe goes along the floor joist into the unfinished room and then shoots straight up. I went up in the attic and can see that this pipe is connected to the main vent that goes through my roof. Like you suggested, I'll run a pipe straight up from the old lav location to this pipe to vent the tub and toilet and also tap into the pipe from my new lav to vent that.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Venting a basement bathroom
[ 1 Answers ]
Hi we are putting in a basement bathroom, and I was wondering about the venting. THe basement bathroom will be directly below the upstairs bathroom . Do I just hook my basement venting into the line that runs from the upstairs or do I rum a whole new pipe through the roof? And where should I...
Basement Bathroom Venting
[ 1 Answers ]
My question is about venting my basement bathroom group. The builder roughed in for a bathroom and it seems that the 2 inch pipe behind the toilet hole is the vent pipe. Can I simply connect this to the capped off 2 inch pipe the builder left with the label "air vent" written on it and would this...
Basement Bathroom Venting
[ 2 Answers ]
I had my rough in inspection yesterday, and everything looked good except my venting for my sinks. I am installing a bathroom lav and a wetbar sink, running into a 2" wet vent that already has a tub/shower on it. Since the distance to the furthest sink is just under 5' from the wet vent I thought...
Venting a basement bathroom
[ 7 Answers ]
I have a rough in for a full bath in my basement.
House was built in 2000 in Pa. Two story colonial.
I can locate two vents from the 1st floor bath. One 2" vent right of the WC drain and one 1.5" off the shower on the first floor. There is a 2nd floor bath over the first. I can hear the 2nd...