    Wire size
    What size aluminum triplex wire should be used to supply 2 200 amp services 150 feet from transformer pole ?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jan 12, 2008, 06:33 AM
    Seems your question got missed.


    This is not really practical to try to deliver 120 volts at 150 feet and have the capacity for 400 amps. Assuming the maximum load of each 200 amp service to be 80% of full rating, would mean the calculations would be based on 320 amps, or 160 amps for each service entrance.

    So each service should be treated separately.

    Each service will need a minimum of #4/0 aluminum to keep the voltage drop below the recommended 3%.

    Check with your local utility. My local one recommends a 200 amp service can use #4/0 up to 215 feet, based on the same Vd calcs and tables published by the NEC.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

What size wire? [ 10 Answers ]

I'm wanting to run power from my home to a pole barn that I recently built. I plan on running 110 and 220 outlets. What size wire should I use to run from the house to the building itself? I do plan on running from the main supply and going to a separate breaker box once in the building. I'm...

Wire Size and panel size [ 6 Answers ]

I have a separate small living quarters that is a single room that is about 180 feet away from the main panel. It is going to get another little bed room a small kitchen and a bathroom also maybe a washer. The main panel is a 100 amp meter socket combo. What should I upsize the main panel to? ...

What size wire? [ 3 Answers ]

For a run of #2 electric wire, in conduit, what size neutral and what size ground wires should I use? It's about a 50 foot run.

Wire size [ 2 Answers ]

I am wiring a barn/shop fed by a 100 amp service. Some of the outlets may be over 70 feet from the panel (all will be 20 amp breakers). Should the wire size I pull in for these outlets be 10awg rather than the normal 12awg? My question relates to voltage drop. The shop is about 50'x 70'. Two big...

4 wire home service entrance wire size [ 1 Answers ]

Mobile home requires 4 wire electrical service entrance wire. Distance is 160 foot from meter to breaker panel. 220V service. What size wire do I use? Can I use diff. size for neutral and ground?


View more questions Search