    furnaceman's Avatar
    furnaceman Posts: 1, Reputation: 1
    New Member
     
    #1

    Jan 7, 2008, 10:05 AM
    Trane xe 80 burner will not ignite
    I have a forced hot air Trane xe 80 furnace. Electronic ignition. At times the burner will not ignite. The fan motor runs and only cold air is coming out. If I turn the furnace switch off then on again, it will glow and then the burner will ignite. This could last for days, then it will do it again.
    therinnaiguy's Avatar
    therinnaiguy Posts: 153, Reputation: 5
    Junior Member
     
    #2

    Jan 8, 2008, 06:38 AM
    Here a few things to check. Trane has a screen in the air intake port of this furnace. It blocks any debris from entering the combustion chamber. I have found that if a leaf got to the screen and as the temperature dropped, Ice started forming and increasing the size of the restriction to the point where the furnace just stopped. Really! If you experience the no-heat condition on days when there is ice in the air or the temperature dropped suddenly, you may have this condition. Take a very powerful flashlight, one that you can focus the beam and look up through the viewing window at the top of the burner box. By looking at the bottom of the center pipe, you will see lots of small round holes. This is the screen. Focus the beam to see if you can detect any debris caught on the top side of that scree. If so you will need to remove the center PVC pipe from the top of the furnace and clean out the debris. Because this pipe is the fresh air coming into the furnace, It is fine to not glue it back into place but seal the outer edge only with some silicone. You will find that you may need to cut the old pipe about 2" above the furnace to be able to access it. If so, just get a new coupling and pop it in.

    If it continues, you may be looking at either a build up of water in your venting system or a weak circuit board. Make sure the venting system pitches back toward the furnace so any accumulation of water gets drained out through the condensate drain. Clear away any obstructions from both the air intake and exhaust pipe outside and check to see if you are not sucking the exhaust air back in as the furnace runs.
    lemp0005's Avatar
    lemp0005 Posts: 5, Reputation: 1
    New Member
     
    #3

    Jan 22, 2008, 08:10 PM
    Try cleaning your flame sensor with sandpaper.
    montyg's Avatar
    montyg Posts: 17, Reputation: 2
    New Member
     
    #4

    Jan 23, 2008, 07:38 AM
    I have/had the same problem with my xe90. Changed PC boards only to get another but similar problem. I eventually discovered that there was NO ground on the unit and after running a wire to the water pipe the problem seems to be fixed, hopefully. The PC boards are extremely sensitive to polarity and the ground and can actually eat themselves up over time if not grounded. This is something I would check... Good luck.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Main Burner Won't Ignite [ 3 Answers ]

I have a small furnace that heats my garage and two rooms above my garage. Turned this furnace on for the first time this year and all it does is blows out cold air. Pilot is lit but it seems like the main burner doesn't ignite. Any ideas? Thanks, Gerry

Circuit board? Or something else? Burner fail to ignite [ 3 Answers ]

Greetings all, I can't believe I am here again. Anyway, my Lennox G27M is not working again. (it's almost 10 yrs old, a two-stage gas furnace and 80% efficiency.) This time, the code is saying that the burners fail to ignite. So I have a hvac tech over and he did some checking with the volt...

Gas furnace burner won't ignite [ 5 Answers ]

I have a 26 year old Friedrich gas furnace model GHA075NDC that the burner will not ignite. The pilot is lit and I can turn the fan on, but the burner will not ignite. Can anyone help me solve this problem?

Ignitor will not ignite [ 7 Answers ]

I have a intertherm honeywell furnace about 6 years old and the ignitor will not ignite so furnace will not turn on... I put in a new ignitor in but still will not ignite... Is anybody out there familiar with this problem and can direct me in the right direction... Thank you very much... Paul

Quote on 2 1/2 ton Trane XR13 and var spd Trane Blower [ 2 Answers ]

I was just quoted on a 2nd floor A/C replacement, condenser and var speed blower, 2 1/2 ton Trane XR13 with upgrade options. Live in CT Are these prices sane ? Includes removal of old unit, upgrade of refrig line, added insulation on old ductwork - work to be done in walkup attic Quote...


View more questions Search