    Recessed lighting romex
    Very quick question... I am installing recessed lighting. Total of 7 cans that will house 60 watt bulbs.
    Should I use 14/2 or 12/2 romex to between cans? It is a 15 amp circuit and 14/2 enters the original junction box.

    Thanks.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #2

    Jan 6, 2008, 06:24 PM
    7 X 60= 420 Watts.
    420/120= 3.5 Amps
    Figure 1440 watts for 15 amp circuit.(15 X 120 =1800 X.8 = 1440 watts continuous).
    Divide 1440 by 60 watt bulbs, you get 24 bulbs.
    With #12, and 20 Amp circuit, you could have 32 Bulbs.
    Maybe have lighting on own circuit, to prevent an outlet tripping, leaving you in the dark.
    Sailorman's Avatar
    Sailorman Posts: 33, Reputation: 1
    Junior Member
     
    #3

    Jan 6, 2008, 06:33 PM
    So I should use 14/2 romex?
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #4

    Jan 6, 2008, 06:40 PM
    What he is saying as longs as it is less than 24 bulbs, OK. So #14 is plenty good for 7.
    Cobraguy's Avatar
    Cobraguy Posts: 140, Reputation: 11
    Junior Member
     
    #5

    Jan 7, 2008, 06:30 AM
    Since his circuit originates with 14/2, the use of 12/2 would be of no value. The circuit MUST be protected with no more than a 15A breaker.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Recessed Lighting on Dimmers [ 2 Answers ]

I have a 15 amp circuit dedicated for 16 6" Halo IC recessed lights in my basement. To control these recessed lights, I installed one 3 way dimmer that controls 8 of the recessed light and the other 8 recessed lights are controlled by a regular single switch dimmer. Currently both dimmers work...

Recessed Lighting [ 8 Answers ]

Need help with Recessed Lighting. The included picture is an electrical diagram I used in wiring up some recessed lighting. The switches used are 600w Dimmer Switches with push on/off feature. The problem is that on the center switch the dimming feature burns out consistently but I am still able...

Suspended Ceiling / Recessed lighting [ 5 Answers ]

I have a "problem" suspended ceiling. I bought a house almost a year ago, and I knew that at some point the suspended ceiling in the basement would become a frustratiion. The finished room is about 10x21 feet. It is a USG ceiling with 2x4 USG ceiling tiles. The issue is that the ceiling is hung...

Recessed Lighting in Suspended Ceiling - Romex OK? [ 1 Answers ]

Hey guys, I've got a question for the experts, I'm finishing my basement and putting in a suspended ceiling. Can someone tell me if it's OK to run Romex to the recessed lights I'm putting in with the ceiling, or do I need to place j-boxes on the joists above with Romex between them supported...

Recessed lighting for playroom [ 1 Answers ]

I have a 11X14 bedroom which I am converting into a playroom. I want to install 6 inch recessed cans. I would like to know how I should layout this room using either six or eight cans. Any help and/or suggestions is appreciated.


View more questions Search