    Heat pump wiring?control board
    I got a call for replacing a T-stat... (for home). The York heat pump... after replace with the new one. I found the blown fuse at the airhandler... changed... now I have the blower up and now the electric heat is temporarily used but the unit outside is not running...
    In heating mode : the unit outside not working
    In Cooling mode : the unit is working fine...
    Q1/ May I have a wiring wrong? With the old t-stat O, B are connected to terminal. With the new t-stat O can connect but not B... so what I should consider?
    Q2/ I push the reset button at the unit (contactor) outside in heating mode the unit run fine with Low side = hot... and I release the reset button the unit stop working... So board is defective?

    Any advices... thank you.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Dec 13, 2007, 12:37 AM
    Sounds like your signal circuit is not making it to the heat pump to activate the contactor. It could be something with the thermostat since you just changed it.

    Look at the sticky notes at the beginning of the board to help determine the what the wiring for the thermostat should be.

    You did not post the model of the new thermostat. Do so now.

    The thermostat you bought to replace the old stat with might not function with a heat pump.
    charlot's Avatar
    charlot Posts: 3, Reputation: 1
    New Member
     
    #3

    Dec 13, 2007, 01:45 AM
    I did check the wires color at the unit to t-stat...
    The new T-stat that I bought is not good for this type of heat pump. Like you said: I will looking for another one especially for heat pump.
    Thank you for your help... I will let you know the result tomorrow.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

NO HEAT! Janitrol heat pump and AC system. Changing to Lux Thermostat. Wiring issue. [ 11 Answers ]

I have a Janitrol A/C and heat pump system. I replaced the thermostat with a Lux T9000LC The A/C works fine, but the heater does not. I have it wired as follows: G - Green Y - Yellow W - White RH - Pink B -

Dual switchable thermostats for heat pump control at night. [ 6 Answers ]

I would like to have my heat pump controlled by the centrally located main thermostat during the day, but switch to a different thermostat located in my bedroom during the night. Is this possible and how would I go about wiring it? I was hoping it may be a readily available kit?

Wiring fan from thermostat to control board? [ 10 Answers ]

Hi all. I just installed a new thermostat thinking this would solve my problem of not being able to engage the fan using the old thermostat (using "on" or "auto".) I was wrong. I'm getting the same behavior with the new thermo. According to another HVAC forum, it turns out the reason I...

Heat pump control [ 1 Answers ]

I have Lennox heat pump about 10 year old. The control center is called Harmony II. There is a red light which has been on/off for a few years now. The mannuel says it indicates need of service. The service contractor tried very hard and could not fix it or find out why (I do not have...

Wiring question for new blower control board [ 1 Answers ]

Just bought the Lennox blower control board replacement kit - 31M73 I'm stuck on wiring the transformer--- The five wires coming out of the transformer going to the old board are - Yellow - common Blue - 24 vac Orange-L2 XFMER Primary Black - L1 XFMER Primary Red - PARK


View more questions Search