    How to ground a GFI outlet?
    Here in OH, the label on GFI "NOT GROUNDED" is no longer acceptable. There are only Hot and neutral lines in the box. The box is not grounded. What options do I have?
    If I have to run a new ground wire to the breaker box that is 60 amp. Is the new wire attached to the neutral bar in the box?
    Thanks for the help
    Tim
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Dec 12, 2007, 09:52 AM
    On a three wire service entry, the Neutral will be tied to ground.

    Are you referring to a GFCI Breaker or a GFCI receptacle?
    timur's Avatar
    timur Posts: 3, Reputation: 1
    New Member
     
    #3

    Dec 12, 2007, 10:18 AM
    This is a GFI outlet in an older house with 60amp service and has only 2 wires.
    Thanks for the help
    Tim
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #4

    Dec 12, 2007, 11:13 AM
    I think your only choice is to pull a new XX-2 with ground. Your panel should have separate neutral and ground bars, tied together only at the main panel. Any equipment grounds you have should be tied to the ground bar. If you don't have a ground bar, I hope you at least have a couple of tapped holes to fasten one too.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #5

    Dec 12, 2007, 11:43 AM
    Quote Originally Posted by timur
    This is a GFI outlet in an older house with 60amp service and has only 2 wires.
    Thanks for the help
    Tim
    So the service you have is only 110 volts? It has to be if it is only 2 wires. You can take the ground tab on the GFI to a grounded water line last time I heard. Usually a water line that is grounded will allow the imbalance to be detected by a GFI. Check with the NEC national Electric code under exceptions.

    ((If I have to run a new ground wire to the breaker box that is 60 amp. Is the new wire attached to the neutral bar in the box))

    Do you have a ground rod on site now? Usually the old 110 systems still required a g-rod. If you have one it should be landed on the neutral bar in the box. Many times the ground rod was taken right off the meter base and located right under the meter base so no ground was visible in the service panel..
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #6

    Dec 12, 2007, 02:49 PM
    Timur, that is an interesting requirement. Just for education purposes, can you show the source of that? I don't doubt you, but that is a very costly requirement to implement. And sometimes not practical. I hope they offer suggestions to comply. I will try to find this info at the state website, if you can direct me I will appreciate the time savings.

    A ground rod is not always used, esp with older homes fed by metal city water lines. You may also find a grounding conductor clamped on at the water meter.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Sharing the ground on a 240 outlet [ 3 Answers ]

Hi. My first time asking a question but thanks in advance! I am adding some additional outlets to an existing fuse. This is for professional audio equipment, so I am trying to get the best grounding possible. There is a 240 outlet in the basement where I am adding these circuits. It is...

Connecting ground to 220v 3-wire outlet [ 8 Answers ]

I am trying to connect my bandsaw to an old-style 3-wire 220v dryer outlet (2 hot wires, 1 neutral). My bandsaw has no neutral wire. Do I connect the ground from the machine to the neutral socket?

How can I ground an outlet? [ 7 Answers ]

We just rented a house (built in the 70s I believe) and as we were moving in we noticed there are no 3-prong outlets in the living room, there is one in each bedroom though and 2 in the laundry room. We had planned to put our computer in there and we really need the outlets to be grounded. We had...

Electrical Outlet - No Ground [ 3 Answers ]

Got back from vacation and refrigerator was out. When testing the outlets it reads "No Ground". Replaced the GFI outlet and still reading "No Ground". The breaker never tripped. All wires on the outlets to that circuit are secure. What could be the problem?

No ground switch and outlet replacement [ 5 Answers ]

I have an old home built in the 50's with original wiring that does not have a ground. If I want to replace a switch do I need to some how run a ground to it or can I just replace the switch with a new switch (the way the wiring is currently)? If I want to replace an outlet I have to use a...


View more questions Search