    Circulator pump works but oil burner does not fire
    Hello,

    I have a 2 zone heating system, forced hot water with oil burner/boiler. Also heats domestic hot water tank/coil.

    Everything works fine EXCEPT zone 2, which is only the living room. When the thermostat is turned up, the circulator pump goes on but the oil burner will not.

    The system has all Honeywell parts... RA832a relay for zone 2, L847 box for zone 1, aquastat for domestic water tank, and stack relay RA117.

    I don't know where to begin because the system works in zone 1 and for the domestic water. I've had service tech out here but he couldn't find the problem.

    Any help is greatly appreciated... thx
    Rich
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Dec 7, 2007, 04:51 PM
    Here is a wiring diagram for you.

    http://customer.honeywell.com/techli...0s/69-0791.pdf

    If one zone is not working then isloate your trouble shooting to it.


    The RA832A has two sets of contacts. One can be used for the circulator and the other for the burner. I believe one set of contacts ( for the burner in the boiler) to be defective. If so you will have to replace the control. I would also recommend you find a better repair person than the last one to diagnosis this defect and to replace this control if necessary.
    Rekka213's Avatar
    Rekka213 Posts: 6, Reputation: 1
    New Member
     
    #3

    Dec 7, 2007, 05:00 PM
    Of course you are right... inside the RA832 the circulator and thermostat wires are connected as well as the hot line coming from zone 1 relay box.

    Is the problem where the RA832 connects inside the boiler?

    Thanks for response!
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Dec 7, 2007, 05:24 PM
    The boiler works. The problem has to do with the ONE circuit that is not working. The box in the boiler works on the one zone so it should be OK.

    In other words the burner is not getting a signal to light off and burn when the thermostat calls for heat. But the circulator works so the problem is isolated to the burner/controls for that zone.

    You need a meter and know how to use it in order to track the problem down. This time get a guy who knows about boilers to find that problem for you. At least you are now partially armed and dangerous so do not let the repair man rip you off. If they cannot find the problem do not pay them since they could not fix it and call someone else until you find the right person for the job.
    Rekka213's Avatar
    Rekka213 Posts: 6, Reputation: 1
    New Member
     
    #5

    Dec 7, 2007, 05:38 PM
    Thanks hvac1000 for the good advice.

    I am an amateur with a mulitmeter and was hoping to fix problem myself but am not that sure of the electrical controls, is this something I can do myself?


    Thanks again!
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #6

    Dec 8, 2007, 08:56 AM
    If you do not know what you are doing it might be better to seek professional on site help.
    ChasB's Avatar
    ChasB Posts: 1, Reputation: 1
    New Member
     
    #7

    Dec 1, 2010, 11:09 AM
    Check to see if the #2 zone valve is opening when the thermostat is turned up. Touch the pipe on both sides of the valve. The pipe should be equally hot on both sides of the zone valve. The valve could be faulty. It is also possible there is a restriction in your zone #2 such as air in the line or a frozen pipe. ChasB

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

My heat pump AC works but not on heating cycle [ 2 Answers ]

I live in a 2-story house in AZ and there are 2 Lennox (sic?) heat/AC pumps, one for each floor... it has 2 Honeywell TH8000 thermostats. Last winter there wasn't any problems but tonight it started getting cold so I turned it from cool setting to heat, I can hear relays in the TS click and it says...

Intertherm model #1265 burner won't fire up [ 2 Answers ]

Pilot is lit,blower works,stat is good,burner will not kick in

Burner does not fire up when heat turned on [ 3 Answers ]

Hi, I have a Lennox Furnace, when you switch on the thermostat to heat and adjust the temp. accordingly, the burner does not ignite. Pilot flame is working, fan works. But no flame on the burner. Here is how the thermostat is wired (Is it right? ) RC- blue wire, G- black wire Y- red wire W-...

Well pump works until 30 lb then drops to 0 [ 4 Answers ]

I have a new 6"well 160 feet deep.Pump is installed at 145 feet.Amtrol wx203 tank is charged to 28 lbs. for a 30-50 pressure switch.running kitchen faucets or lavatory faucets pump works wonderfully.Symmons temptrol shower valve with 2-1/2gpm showerhead runs fine until gauge reaches pressure cut in...

Circulator pump not spinning [ 2 Answers ]

I have an oil furnace plenty of oil and power to everything, but the circulator will not work. It hums when I turn the t-stat up. I would like to repair it. I cannot afford to replace it today -- and pay emergency service prices.


View more questions Search