        Electric Furnace
       
      
    
    
    
                  
        My electric furnace will work perodically, I'm not sure of the brand or model, it's in a 1986 doublewide. It will run and heat fine for a few days, and then it will just stop for a day or so, then start again. Inside the furnace panel I can hit the rocker switch to the ON position, instead of AUTO and the fan runs fine, but no heat of course. I assume it's not the fan. I can't seem to find a trigger to make it come back on until its ready to. Could it be the wire running from the furnace to the Thermostat? Maybe a bad connection or something? Any ideas?
     
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                  | 
            
      
              
               Ultra Member 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      Dec 5, 2007, 04:41 PM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
        Jumper the white and red wires at the thermostat or tie them together, does the furnace come on and work normal,, This bypasses the stat and it will run until you untie them .if this happens you prob. Need a thermostat,, if it still doesn`t work then you no it's the furnace that needs looked into,
     
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                  | 
            
      
              
               Uber Member 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      Dec 5, 2007, 05:47 PM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
        Intermmitent operation often is a bad connection.  Iagree with most of the above, but you may just need to tighten the wires rather than replace the thermostat.
     
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                  | 
            
      
              
               New Member 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      Dec 7, 2007, 12:17 PM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
        Actually, I have already replaced the thermostat because it was doing this. That didn't seem to fix the problem. Could it actually be the wire running from the furnace to the thermostat? Or, something within the furnace?
     
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                | 
            
      
              
               Heating & Air Conditioning Expert 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      Dec 7, 2007, 04:44 PM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
        More than likely it is a defective sequencer in the furnace causing this problem. You will have to test the sequencer when the problem is happening to check for current flow. 
 
A sequencer can have many jobs. They can bring on the fan,activate the heat,act as a time delay. Your furnace should have a wiring diagram on the inner part of the door to help you find the part. Many times heat /blower sequencers are intermittent.
     
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                  | 
            
      
              
               New Member 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      Jan 4, 2008, 10:35 AM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
        Bingo! That seemed to fix the problem. I replaced the sequencer and it's been running fine without any issues.  
 
Thanks.
     
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
 
 
 
     
  
   
  
   
  
  
  
  
  
  
  
  
  
  
  
  
  
  
    | Question Tools | 
    Search this Question | 
   
  
    | 
    
    
    
     | 
    
    
    
    
    
     | 
    
   
   
   
    Add your answer here.
    
    
 
Check out some similar questions!
York Electric Furnace
 [ 9 Answers ]
My York Electric furnace will not stay on.  It runs for about 5 minutes then 
Shuts off.  We do have heat, just temporarily.
 
 
Nordyne e2 electric furnace with ac
 [ 1 Answers ]
Hello I have an nordyne e23h012hn electric furnace, the control board is burnt and evaporator fan will not come on, replaced board and it burnt up to. The circuit on the board that burnt is the common line voltage to the fan, could it be the fan motor shorted causing this problem . Thanks chris ...
 
 
Electric furnace
 [ 1 Answers ]
I can hear the furnace trying to come on. I hear an elctric switch come on for about 1 1/2 seconds and the stop. It keeps on doing this. What do I do?
 
 
 
View more  questions
Search
 
 |