    Can anyone help with how one might pull an unused 220 amp circuit breaker and put 2 110 breakers in its place? Can it be done?
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Dec 3, 2007, 12:16 PM
    Yes, you can remove a 240 VAC breaker and replace it with 2 120 VAC breakers.

    The work would involve a knowledge of electricity and the NEC codes as well as Electrical Permit.

    If you are not experienced with electrical work inside of the main panel box, stop now and call a licensed electrician.

    If you choose to go on then: Step one is turn the 240 VAC breaker off. (If you are not sure where to put your hands inside the box - turn the main breaker off) Remove the Panel Box's top cover. Then, push Away from the Center) and rotate (Down in the back, up in the front) the double pole breaker. The 120 VAC breakers are replaced by reversing the previous instructions.

    Now, while the 240 Breaker is in your hands, remove the two load bearing leads Black and Red (If you are using a 4 wire installation) or White (if this is a 3 wire installation). Next, remove the White wire from the Neutral Bus bar and Ground wire (4 wire) Green or Bare to the Neutral Bus Bar.

    Now both the breaker and the cable feeding the upstream load are loose. Place the breaker to the side.

    Now it's knowledge time, you need to know the load size (amperage) of the desired devices that you want to replace on the two new breakers.

    If the maximum amperage is to be 15 amp (breaker) or 20 amp (breaker), then you need to either remove the 240 VAC wire from the wall and install a new conductor of 14 AWG or 12 AWG. 4 AWG is used for 15 amp and 12 AWG is used for 20 amp.

    Install the new wire and receptacle per NEC Code. Turn the breaker back on and then test the new receptacles that you have installed.

    Please note that because you are removing a breaker and its associated conductor and then installing two new breakers and their associated conductors and receptacles, you should get a permit and have the work inspected.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Difference between a Power Distribution Unit (PDU) and a Remote Power Panel (RPP) [ 1 Answers ]

Is there any difference between a Power Distribution Unit (PDU) and a Remote Power Panel (RPP) in context of data center? If yes, then what is it?. Thanks.

Wiring a sub panel [ 5 Answers ]

I am installing a small 120v sub panel in my basement. The builder pre-wired from the main service panel a #10 four wire (red, white, black & ground) to my basement. I purchased a small Square D panel and two 30 amp breakers. The box I purchased has no ground bar, only a neutral bar. I know that...

Square d sub panel [ 29 Answers ]

I am not to familiar with residential wiring and I have a question about sub panel problem. I have a 200 amp main panel with a 125 amp sub panel. There is a 60 amp feeder from the main for the sub. My problem is I am getting an unbalanced loading problem. I tried balancing the load between the 2...

Wiring to sub-panel. [ 1 Answers ]

Will this work properly if when wiring a sub-panel for 240v can one of the 3 aluminum 4 gauge wires in the pvc underground pipe be used as the neutral wire if that wire is bare? I intend to attach the ground bus at the sub-panel to a ground rod using 6 gauge bare copper wire.

Power Distribution Units & Remote Power Panel [ 1 Answers ]

What is the basic functionality of these equipment ? What is differnce between PDU & RPP.


View more questions Search