    Adding a sub panel in new addition
    Hi all,
    I'm looking for some information about adding a new sub panel (125 amps) to a addition, which will have a hot water tankless heater (220 vac) and propane furnace (125vac) along with some lights, ref. and oven. Currently, I have a 200 amp service in the main house and this new panel will be mounted about 36' away from the main service. Any advice on wire size and grounding methods.

    Thanks
    Jeff
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Dec 3, 2007, 06:59 AM
    I would recommend using #1/0 Aluminum 4 wire SER cable, which is the size allowed for a residential 125 amp feeder.

    No special grounding is needed, only keep the neutral bar insulated and isolated at the subpaenl, install a separate equipment ground bar in the subpanel, bolted directly to the metal box using machine screws. Use the neutral bar for white neutrals only, and use the equipmnet ground bar for green or bare equipment ground wires, including the one in the SER cable.
    Cobraguy's Avatar
    Cobraguy Posts: 140, Reputation: 11
    Junior Member
     
    #3

    Dec 3, 2007, 07:14 AM
    You might want to check out your tankless water heater. Some of those are huge power hogs. (100A or better) Will your existing service support that along with everything else you have in the home?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Adding a sub panel [ 6 Answers ]

I'm finishing my basement which will have a 60x20 room and a 10x9 bathroom. I'm running 20 amp breakers,12-2 wire, 20 amp outlets. 2 breakers for 20 outlets ( 10 outlets a breaker). 1 breaker for 8 2x4 flourecents. 1 breaker for GFI ( for my freazer).

Adding a sub panel [ 1 Answers ]

I am adding on to a small hunting cabin. The existing electrical panel is essentially a sub with six 20 amp breakers, three active and three spare. Leading into the panel I have one 12/2 wire and one 12/3 wire which were placed there for future use. My question: If I need more than the three 20 amp...

100 Amp Panel sufficient for electric range addition? [ 3 Answers ]

I have a 1200 square foot 3-bedroom house that has a 100 amp panel. Because of rising gas costs I've had an electrician install a 40-amp plug in the kitchen for use with an electric range. My question is a straightforward one, is 100 amps sufficient for this changeout? My dryer is electric and...

Sub panel for garage/addition [ 24 Answers ]

Hey guys I am working on an addition to my home and was hoping to get some advice on the sub panel I plan on installing in the new garage. The existing house is 200 amp service and about 3500sq/ft. I will be adding an additional 1800 and will include the following: 2 half baths 2 full baths 2...

Adding sub panel [ 8 Answers ]

Hi All, My current breaker panel is a Murray Arrow / Hart. It has two rows of 8 sockets each plus three that are taken up by the main 100 amp breaker. All of the positions are filled on the panel, I have even removed the old 240v line to use those two spaces for additional breakers. I have...


View more questions Search