    Blower starting and stopping operation
    I have a bryant gas furnace. It was installed in May of 1995.

    It appears that the blower kick on first. Then the burners are lite. The burners run a while and then turn off but the blower stays on. Then the burners are lite again. The burners run a while and then both the burners and the blower turns off.

    Is this normal operation for a furnace.

    Thanks for any help.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Nov 28, 2007, 05:23 AM
    Clean the pilot sensor.
    laststarfighter0's Avatar
    laststarfighter0 Posts: 3, Reputation: 1
    New Member
     
    #3

    Nov 28, 2007, 01:54 PM
    I will look on the internet to see where the pilot sensor is located. I like the pilot lite via a tube. Is the pilot sensor close to this. I lite the pilot light each year.

    What is involved in cleaning a pilot sensor?

    Is this something that should be done by a professional?

    Thanks for all of your help.

    John
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Nov 28, 2007, 02:45 PM
    The furnace you have must be older than a 1995 model if you have to manually lite the pilot. Did regard the cleaning of the pilot sensor.

    Check you air filter to be sure it is clean to start with. Make sure all register vents are open. It seems like your high limit may be going off causing the blower and burner operation problems and I am just making sure nothing is restricting the system.
    laststarfighter0's Avatar
    laststarfighter0 Posts: 3, Reputation: 1
    New Member
     
    #5

    Nov 29, 2007, 03:22 PM
    I want to thank you HVAC1000 for your help.
    Your suggestion was right on the money. The problem I was having was caused by the air filter. It was NOT dirt but I bought a more thicker air filter. The thicker air filter said it was more effective then flat panel sun glass filter. And it was a ASHRAE Rating MERV8. I replaced it with a thinner Flander Precisionaire Air Filter that I have used before and it started working like normal.
    The blower comes on, then the burner is lite, and then the burner goes out off and the blower runs for a few minutes more and then both are shut off.
    Thank you again for you help. It saved me an heating / Air call.
    Have a good holiday.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Blower during furnace operation on electric Coleman Evcon [ 2 Answers ]

I just installed a programmable thermostat for an electric Coleman Evcon furnace. Now when the furnace comes on the blower also comes on. Sometimes the blower goes off a minute or so before the furnace stops. It never did this before- in fact I didn't even know there was a blower. Do I need to...

Blower moter has trouble starting [ 2 Answers ]

Hello. I have an older central Lennox furnace/air conditioner unit that has been giving me trouble lately. I noticed one day that the blower should have kicked on. I went downstairs and found the motor to the blower was humming but the blower was not turning. I flipped the switch on the unit on...

Intermittent Blower Operation [ 1 Answers ]

Sometimes, the air handler blower does not run when the condenser unit turns on. Setting the blower to ON does not help. When the blower does turn on, setting it to ON will keep it running when the condenser cycles OFF. What could cause this problem?

Blower not starting [ 1 Answers ]

I have a Intertherm M1M model. The blower will not start on it's own you have to manually turn it to get it started. Even then some times it don't blow as hard as it should. Do I have a bad blower motor or is there something else that could be the problem?

Intermittent blower operation [ 3 Answers ]

Hello, I have a Janitrol model A30-08 furnace. On the AC side, when the thermostat calls for cooling, sometimes the blower kicks on, sometimes not. The evaporator coils always cool down (to the point of icing if I don't intervene), so that part is working fine. When the blower doesn't come on,...


View more questions Search