    The draft motor runs continiously
    Hi,

    I have a 80% efficient furnace and I am having the following trouble with the heat.

    The draft motor starts running the moment I power on the furnace. Its had been running during the summer time also when the I just was using AC. Being new to these things I did not realize that it was a problem.

    Issue:
    When I power up my furnace and it reaches the set temperature, thermostat instructs the furnace to stop, and it stops. However, The draft motor keeps running.

    When the thermostat instructs the furnace to start, the furnace LED indicator blinks three times (which is described as "pressure swtich failed to close"). However, at that time if I power off the furnace and wait for few seconds and then power it on again, it works until next time the thermostat tells it to stop. I have to manually do this every time I need to heat my house.

    Any help is appreciated.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Nov 28, 2007, 05:30 AM
    Probably a defective pressure switch. Test it.
    diyperson's Avatar
    diyperson Posts: 5, Reputation: 1
    New Member
     
    #3

    Nov 30, 2007, 01:20 PM
    Thanks for your response hvac1000.

    Can you provide more details on how to test the pressure switch ?

    Can the furnace start up in the first place with a faulty pressure switch?

    Thanks again !
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Nov 30, 2007, 02:08 PM
    Usually there is a round metal object with a tube going to it. Remove the tube and blow through it to make sure it is clear. Next take a meter and check for voltage going through the switch. Just use the frame as ground and test both sides of the switch with one side of the switches wires removed. This will tell if the switch is stuck closed.

    Another way and a bit safer is to remove the wires off the switch and mark them as to where they came from. Then use a ohm meter and measure across the contacts. If the contacts are closed you know you have a bad pressure switch. NOTE the power should be off anytime you are removing wires or testing with a ohm meter.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Furnace's draft motor keep running [ 5 Answers ]

Hi, My furnace recently starts acting weird. After running up to satisfied temperature, the thermostat stops normally, then the blower stops 30 seconds later as usual, but the draft motor sometimes keep on running forever. Turn off then on the power to furnace obviously reset it to normal,...

Goodman furnace induced draft motor [ 3 Answers ]

On a call for heat the draft motor starts but the air proving switch does not close. I replaced it with the same result. Everything works normally if I close the switch manually with my own air pressure. Someone told me that somethimes the motor, due to age (this one is 13 years) will not spin fast...

Blower motor runs slow [ 2 Answers ]

I have a Luxaire Furnace with a/c, blower motor on furnace runs but very slowly, what would cause this, units are about 9 yrs. Old, motor starts slow and stays slow

Draft fan runs always [ 1 Answers ]

Induce draft fan is on all the time, What can I check so that it will operate the right way?:p

Furnace motor runs but no air coming from registers [ 11 Answers ]

Have a Goodman GUPS 100-3 Furnace. I can hear the motor turn on when the temp goes below where the thermostat is set - but no air is being blown through the vents. (I have a forced air systerm.) The vents are OK since my air conditioning unit goes through the same vents. The pilot light stays on...


View more questions Search