    Basement Rough in---Brian
    Hey Tom/speedball,

    I saw you had answered a question online regarding some basement plumbing and I had a few questions myself.

    I dug a trench and hole for my basement as the image will show. I was curious as to what I will need to do to ensure things are properly vented and sized. I want to say the main line is 3" but maybe 4" regardless here goes...

    Shower - What size is doable? Should this use a buried or sub foundation level P-Trap? Is there a danger in burning this P-Trap to far? A scenerio in which water weight couldn't force the water out?

    Sink - Seems pretty standard as it's above ground.

    Toilet - Is there such a thing as a directional Tee?
    Seems from what I've seen the Tees curve in a certain direction.
    Is this what I should use to prevent flow in the wrong direction?
    Is there such a thing as a check valve like set-up I should put in the main prior to the toilet connection?
    Doesn't the toilet have it's own built in P-Trap?

    Do you see any problems in my drawing there?

    Any help would be fantastic!!

    Cheers
    -brian-
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #2

    Dec 2, 2005, 03:51 PM
    Hi Brian,


    (1) Shower--What size is doable? Should this use a buried or sub foundation level P-Trap?

    2" pipe and "P" trap. trap's buried underthe cement and a 2" raiser brought up through the cement to pick up the shower drain. The shower drain wi8ll connect to the lavatory drain and be wet vented.

    (2)Sink - Seems pretty standard as it's above ground.

    Except you will run a vent to the roof off the 2 X 1 1/2" tee you pick it up with.

    (3)"Toilet - Is there such a thing as a directional Tee?
    Seems from what I've seen the Tees curve in a certain direction.
    Is this what I should use to prevent flow in the wrong direction?
    Is there such a thing as a check valve like set-up I should put in the main prior to the toilet connection?
    Doesn't the toilet have it's own built in P-Trap?"

    All drainage fittings direct the flow. You will be using DWV fittings.
    No check valve's are needed in the drainage system.
    The "P" trap's built into the toilet.
    The slope is 1/4" to the foot.

    You do realize that you're getting into major surgery here don't you? You'll need plumbing skills and knowledge to add a bathroom group from scratch.
    You may want to pay a plumber to come in and lay the job out and give you a material list. Lots of luck, Tom

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Basement rough in [ 5 Answers ]

I would like to rough in plumbing in my basement for a full bath (toilet, sink, and shower). I live just outside of Chicago so I suspect the plumbing codes are the same as Chicago. Currently in my basement I have two sump pumps and pits, one pump takes care of the drainage around the foundation...

Basement rough-in [ 3 Answers ]

I've seen a few of the posts w/ similar topics, and I think I'm on the right track. Just looking for confirmation from some experts. The center of the tub rough in drain is about 15.5" from the wall I'm puttting in and about 2" from the back wall I'm set to screw down. Question is, will a std....

Basement rough-in: dap out [ 12 Answers ]

Hello, I've spent the last 3 hours trying to figure out if my roughed in bath is missing something or not and wondering if I am going to have to redo any of my framing. I have the 4" and 2" drains in the toilet area and a 12"x12" dap out for the tub. Well I took the cover off the dap out to take...

Basement rough in [ 3 Answers ]

Hi experts! I'm planning to add a bathroom in my basement but I'm confused about the existing rough in. I've attached two pictures that show the rough in from two different angles. There is one 3" PVC pipe that is about 17" from the wall so it can be used for the toilet. I'm confused about the...

Basement rough in [ 1 Answers ]

Hello, I built my house about 3 years ago and I'd like to finish the basement. The bathroom was setup for a shower, sink and toilet. My question is how to install everything. I have 2 pipes coming up from the floor both 3.5"dia capped. I also have a square patch in the floor for the shower drain I...


View more questions Search