    3- wire thermostat installation
    I am replacing an old Honeywell thermostat. Heat is a natural gas furnace with hot water baseboard heating.

    I have 3 wires: red, white, blue.

    Question: I cannot find the proper thermostat. What type of thermostat do I need? Most store brands seem to be tailored for 2 or >3 wire arrangement.

    Specifically, where does the blue wire go? Without it, the zone flow valve does not close.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #2

    Nov 18, 2007, 07:48 AM
    If I was to guess, I would put red on R, and blue and white on W.
    If old thermostat still works, I would verify switching on old thermostat with meter.
    If fan is able to run with out heat, then blue wire may go to G.
    pelle's Avatar
    pelle Posts: 96, Reputation: 0
    Junior Member
     
    #3

    Nov 18, 2007, 04:12 PM
    Mj

    You state furance than baseboard.. I assume it is hotwater boiler..
    Where are the wires going on the old thermo?
    .. red blue white.. to what terminal.. some older ones used numbers 4, 5, 6 instead of rh, a, w etc..
    If this is baseboard hotwater is it multiple zone?? usually is with 3 wire..
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #4

    Nov 18, 2007, 07:02 PM
    What you need to do is go to the furnace and identify what the wires do. Usually red is from one side of the control transformer, and the thermostat switches it to white on demand for heat and the white activates the furnace. Blue may start the pump or something.
    mjcazzol's Avatar
    mjcazzol Posts: 2, Reputation: 1
    New Member
     
    #5

    Nov 19, 2007, 11:13 AM
    The zone flow control valve has 6 terminals on the back, numbered 1-6.

    Terminals 1,2 and 3: power the valve and connect to the pump

    Terminals 4,5 and 6 connect to the thermostat ( the 3 wire arrangement).
    Terminal 5 powers the valve.
    Terminal 4 OPENS the valve.
    Terminal 6 CLOSES the valve.

    This is where I'm having trouble. The blue wire (extra wire) lands on terminal 6 on the valve, and is needed to close the valve. However, on the thermostat end, I have no idea where to land the blue wire. Every wiring configuration I've tried has the same result... the heat turns on normally, but never turns off. In other words, I'm not putting the blue wire in the right place.

    I'm beginning to think I need a special type of thermostat. The thermostats I've tried appear to only require giving the valve one demand. (fails closed, and power to open. Or vice versa). The common thermostats do not seem to be wired for a valve which requires both a signal to open and a signal to close.
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #6

    Nov 19, 2007, 11:47 AM
    Apparently the old thermostat used a double throw switch to close the valve. What you can do is use a double throw relay. Connect W and the transformer common to the coil. Connect red to the relay common. Connect #5 to the NOC, and #6 to the NCC.
    pelle's Avatar
    pelle Posts: 96, Reputation: 0
    Junior Member
     
    #7

    Nov 19, 2007, 04:29 PM
    Try this config

    Zone thermo
    R or 5 to terminal 'rh'
    W or 4 to terminal 'w'
    Y or b or 6 to terminal 'a'
    The terminal specified would be on the new thermostat.. just went through this at my parents, they have a 40 year old 3 zone valve boiler had old white and rodgers thermos exchanged them for rite-temp check this website
    The RiteTemp Support Site - Zoned System Guide
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #8

    Nov 19, 2007, 09:31 PM
    If this is a White Rodgers 3 wire zone valve you will need a compatible thermostat for the system to work correctly.
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #9

    Nov 20, 2007, 05:07 AM
    The hot water heat at my church works just fine with the zone valves controlled by relays wired up just as I said. It is going to be cheaper and easier to find a relay to make the thermostat you have work, than to find a programmable thermostat that will provide a valve close signal.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

6 wire AC/Heater to 5 Wire thermostat [ 4 Answers ]

Hi, I have a Coleman BRCS0301BB AC and a gas based heting unit. I see 6 wires coming up to the thermosat - Red Blue White Yellow Green Brown

Hooking up a new thermostat but old thermostat has a white and a black wire? [ 2 Answers ]

Everything I look at indicates a white and red wire for the connecting wires. Our thermostat is probably original to our home (1943). It has two wires. It is difficult to tell but it looks like one is a white wire and the other is black. I've tried looking on the internet for some info however...

Installing New Thermostat from 6 wire to 5 wire [ 2 Answers ]

I'm installing a new 5 wire progammable Hunter Thermostat. I have all but one of my wires accounted for. I RH and RC jumped together with R, W2 to W, Y to Y, and G to G. I do not need the "C" common blue wire as the new unit is battery operated, so I have this wire taped off. I have an orange...

5-wire thermostat - LOST a few wire labels. HELP! [ 2 Answers ]

I am installing a programmable thermostat (upgrading from a previous programmable that wasn't to our liking. When taking the old thermostat off, I noticed 4 of the 5 wires were labelled. That's a good thing. HOWEVER, when I took the old baseplate off, 2 of the labels fell off (not sure from...

Wiring a 2 wire thermostat to a 4 wire system [ 1 Answers ]

I have a gas furnace equipped with central air.The compressor is shot in the AC unit,and I needed to replace the thermostat so I bought a heating only thermostat.I have the blower and the w wires together on the w terminal designation and the rh on the r terminal designation, and I have the y wire...