    Flexible conduit limitations
    I am rerouting wires in a condo. The original construction has every wire running through rigid conduit. It would be much easier for me to use flexible conduit for the reroutes. Are there any limitations to the length of a flex run? Can sections of rigid conduit be interspersed when it is convenient? Is steel flex better than aluminum flex? Please note that the wiring is such that all grounding is through the conduit, not through a separate ground wire. Thanks in advance for your input.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Nov 22, 2005, 08:49 PM
    There is no limitation to length, only that there are no more than 360 degrees of bends from one junction box to another.

    Also, flex is not suitble as an equipment grounding conductor, such as the rigid conduit, so a green wire of the appropriate size to the circuit must be installed along with the branch wiring..

    Steel offers more physical protection than aluminum, aluminum is lighter and easier to work with. Not sure of the cost difference at the moment..

    There is even nonmetallic, PVC, flexible conduit to chose from. All the necessary fittings and boxes are available also. May be worth looking at.

    I caution you thou, if this condo is attached in any way to another unit, you may not be allowed to do your own wiring, please check with your local building official for the approval, while you are applying for a permit.
    Borewyrm's Avatar
    Borewyrm Posts: 65, Reputation: 2
    Junior Member
     
    #3

    Nov 28, 2005, 07:36 PM
    Flexible? As in greenfield?

    What exactly are you planning on adding or moving?
    dctobin's Avatar
    dctobin Posts: 1, Reputation: 1
    New Member
     
    #4

    Dec 3, 2005, 11:52 AM
    More Flexible conduit
    But what is the easiest way to thread the wire through the flexible conduit? I am trying to get 14AWG through 1/2" flexible pvc conduit for a run of about 17 feet -- can't get the last 3 or 4 feet pushed through!
    caibuadday's Avatar
    caibuadday Posts: 460, Reputation: 10
    Full Member
     
    #5

    Dec 3, 2005, 01:40 PM
    Quote Originally Posted by dctobin
    But what is the easiest way to thread the wire through the flexible conduit? I am trying to get 14AWG through 1/2" flexible pvc conduit for a run of about 17 feet -- can't get the last 3 or 4 feet pushed through!
    they use nylon or metal snake... or you could drop a pull line in before installation by using a heavy object ( a small metal rod/bolt) and attach a string to it...
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #6

    Dec 3, 2005, 01:41 PM
    Easiest way is to use fishing tape made to pull wires through a conduit. I have had good luck with coat hanger wire on shorter runs. As cheap and easy as PVC is to work with, perhaps cut it and set an ''LB'' at one of the sharper bends.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Flexible Budget [ 1 Answers ]

What is its purpose? eliminate cyclical fluctuations in producation reports by ignoring variable costs compare actual and budgeted results at virtually every level of production reduce total time in preparing actual budget I think it is the second one, does a1 disagree?

Conduit requirements for basement wiring [ 1 Answers ]

I am finishing a basement with stud wall and dry wall. Is there any need for conduit to carry the wires behind the dry wall? I know for an unfinished basement wiring below grade must be in conduit but must it if the walls are finished? Thanks Dschaar

Do I need conduit? [ 4 Answers ]

I have a panel in my garage for my garage based workshop. I want to run a 220 volt circuit (have have the capacity in the panel to do so). My question is whether I need to run the wire inside conduit or can I run romex without conduit. The wire will be behind drywall the entire way so it will...

Conduit sizing? [ 4 Answers ]

Hi all! I am relocating my breaker box approx 30 feet from its original location. Installing splice box in the old location for connections. My question is : I have 14 12-2 and 3 12-3 to pull from new box to splice box what size conduit do I need so not to worry about heat build up or de-rating...

Electrical conduit [ 1 Answers ]

I am running a new exterior line to a carport to install two fluorescent lights in the ceiling of a "V" shaped aluminum 2 car carport. The underside of the carport reaches very hot temperatures during the summer months, metal parts are burning hot to the touch. I undersatnd I need to use exterior...


View more questions Search