    Nov 8, 2007, 05:49 PM
    Hot water turns cold after 2-3mins.
    This problem has just started recently. I run my shower and the hot water becomes cold just after 2-3mins. I've got endless hot water in the rest of the house. I have read through this dicussion board and have noticed much talk about water heaters however have seen little about Tankless Boiler. I've got a Tankless Forced Hot Water Boiler(Weil McLain Gold Series). I have since flushed the boiler, turned up the mixing valve, thermostat set to 170 and still have the same problem. I have slowed down the cold feed to the boiler and have seemed to get more hot water but it doesn't last. The hot pipe out from the boiler is scalding hot (coil OK), the pipe after the mixing valve is hot (mixing valve OK?). Could it be the pressure balance valve being stuck? Any help would be greatly appreciated?
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #2

    Nov 9, 2007, 10:45 AM
    It seems it's not the water heater, but it could easily be the shower valve itself especially if it's temperature regulating. Another possibility is debris in the line.
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #3

    Nov 9, 2007, 11:12 AM
    You may need to turn the temperature down. Check the specs. Your heater has a minimum flow. You crank the valve all the way to hot, and run it until the water in the line is all hot. You then adjust it to a moderate temperature reducing the flow of hot water below the minimum. The heater shuts off, and when all the hot water runs out of the pipe, berrrrrr.

    The more I learn about those things, the happier I am that I didn't blow a fortune on one.
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #4

    Nov 9, 2007, 12:08 PM
    Seems that it is likely your mixing valve if you have good hot water everywhere else in the house. KISS asked if it was a temperature regulating valve, is it? Is your valve an anti-scald valve?
    plumberjames83's Avatar
    plumberjames83 Posts: 99, Reputation: 5
    Junior Member
     
    #5

    Nov 9, 2007, 05:05 PM
    Quote Originally Posted by mklays
    This problem has just started recently. I run my shower and the hot water becomes cold just after 2-3mins. I've got endless hot water in the rest of the house. I have read through this dicussion board and have noticed much talk about water heaters however have seen little about Tankless Boiler. I've got a Tankless Forced Hot Water Boiler(Weil McLain Gold Series). I have since flushed the boiler, turned up the mixing valve, thermostat set to 170 and still have the same problem. i have slowed down the cold feed to the boiler and have seemed to get more hot water but it doesn't last. The hot pipe out from the boiler is scalding hot (coil OK), the pipe after the mixing valve is hot (mixing valve OK?). Could it be the pressure balance valve being stuck? Any help would be greatly appreciated?
    It is probably in your shower on the mixing vavle inside of it if this only happens in the shower
    mklays's Avatar
    mklays Posts: 7, Reputation: 1
    New Member
     
    #6

    Nov 12, 2007, 08:38 AM
    Guys, thanks for the responses. It has definitely got to be in the mixing valve at the shower. What kind of work am I looking at to change over or clean this mixing valve? Should I just be calling a plumber? What is the general charge for a job like this?
    mklays's Avatar
    mklays Posts: 7, Reputation: 1
    New Member
     
    #7

    Nov 12, 2007, 08:40 AM
    Comment on ballengerb1's post
    This ended up being the answer to the problem.
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #8

    Nov 12, 2007, 08:50 AM
    A plumber would likely clean the valve so there would be a service call plus time. Could run about $100 but the job isn't too difficult so give it a try. There are serveral people here who can walk you through the small project. Basically, shut off your main water and open a faucet somewhere to blow pressure. Remove the handle and escutcheon ( plate thing). Now depending on your valve you should see a round plate with 2-3 screws holding the plate to the valve or you may see a nut like ring about the size of a 50 cent piece, remove this to pull the valve or cartridge. Once it comes out look at the bottom for the inlet ports, debris builds up here so pick it clean with a soft small object like a tooth pick. Flush the valve with water and before reinstalling hold a towel over the opening of the valve and have someone open and then close your main to flush an immediate debris from the lines. Most debris is found on the hot side primarily coming from your water heater. Flushed the heater lately, you should.
    plumberjames83's Avatar
    plumberjames83 Posts: 99, Reputation: 5
    Junior Member
     
    #9

    Nov 12, 2007, 05:20 PM
    Just replace the cartridge all together! That's what I do when I go to a house call works 9/10 times the other times cleaning the ports work
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #10

    Nov 12, 2007, 06:45 PM
    Don't know Plumbjames, isn't that a bit like throughing out those dirty dishes and buying new? Cleaning the inlets doesn't cost mklays any money and one less trip to the hardware store. I think we are here to assist DIY projects and help homeowners understand how to keep their homes in good repair.
    mklays's Avatar
    mklays Posts: 7, Reputation: 1
    New Member
     
    #11

    Nov 13, 2007, 10:17 AM
    I checked the cartridge and the pressure balance barrel sounded good but I figured for $46 I'd just replace it with a TA10-3hole and I've still got the same problem. There was no debris in the lines. My question now is -- what else could it be? I've exhausted my efforts and have done everything I can think of, and have become frustrated from doing all this work and now I've got to give it to a plumber to fix what I know will be something I've easily overlooked.
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #12

    Nov 13, 2007, 11:58 AM
    Try running the hot water at a sink until it is hot, and cut back to a trickle, and see if the heater cuts out.
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #13

    Nov 13, 2007, 02:05 PM
    We may just be using different terms but is this a water heater or a combi boiler and what does the tempering valve do and where is it located? I am not familiar with that term.
    Thanks
    mklays's Avatar
    mklays Posts: 7, Reputation: 1
    New Member
     
    #14

    Nov 14, 2007, 10:00 AM
    Out of consideration for your help, I'll let you know that a plumber came by the house to diagnose the problem and spent approx. 25 minutes checking the new valve in the shower, the lines and came to the conclusion it was NOT a plumbing issue and that it had to be the boiler. I then got on the phone to who services my boiler and after a tech. spent approx. 1.5hrs. Checking the aquastat, the mixing valve(boiler) and flushed the system. Result was slightly hotter water to the shower and was told there was nothing wrong with the boiler. This is where I currently stand on the issue.
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #15

    Nov 14, 2007, 10:07 AM
    OK I guess U should have asked this question long ago, how is the hot water at other fixtures? If the issue is just at the shower and no where else it is not the boiler and is a plumbing problem. I'm sure the plumber did this checking when he was out to determine if it is the shower or whole house.
    mklays's Avatar
    mklays Posts: 7, Reputation: 1
    New Member
     
    #16

    Nov 14, 2007, 10:21 AM
    It is a Weil McClain Tankless Forced Hot Water Boiler. Everything checked OK on the boiler. We ran hot water for several minutes and the aquastat on the boiler read the water was heated to 180 degrees coming out of the boiler and then it is the tempering/mixing valve which cools the water to its setting of 140 degrees before going through the lines to the house. After bringing the water to a trickle, the heater does cut out. At the shower, instant hot water after running hot water at the sink for a few minutes and then the water becomes lukewarm/hot but not 140 degrees which is the setting on the mixing valve at the boiler. It seems like a volume issue at the shower with the hot water.
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #17

    Nov 14, 2007, 10:34 AM
    I think I just need to know how the hot water is at all of the other fixtures in the house. Does your kitchen sink run hot water continuously, same for you bathroom sink? I think you are saying the hot water is fine at the sink so I still suspect a plumbing problem at the shower. Back to you.
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #18

    Nov 14, 2007, 10:46 AM
    I am sorry, but I was thinking of how the free standing tankless heaters work, not the combiboilers. With it seeming to be a low flow problem, I was almost right for the wrong reason.

    Have you tried removing the cartridge at the shower and flushing the hot line out good?

    If that doesn't do it, you will need to gather some more information, how does the system respond to low flows elsewhere? It must not respond if you turn the temperature back up in the shower.
    mklays's Avatar
    mklays Posts: 7, Reputation: 1
    New Member
     
    #19

    Nov 14, 2007, 10:48 AM
    Yes, I did tell the plumber it was ONLY THE SHOWER. The plumber had checked the pressure balance valve, checked for any debris in the lines and said they were fine as I had already known since I had replaced the valve.
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #20

    Nov 14, 2007, 10:52 AM
    I think you need another plumber. If the problem is only at the shower IT IS a plumbing problem. I think Labman and I are reaching the same conclusion, it is in the cartridge or the line feeding the hot side of the mixer. The fact that you replaced the valve makes me think there is something in the line, something big.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Cold water coming out of hot water tap in bathroom but Really hot water in kitchen [ 7 Answers ]

Can anyone give me a reason as to why nearly completely cold water is coming out of my hot water tap in my bathroom but when I run the hot water tap in the kitchen the water is nearly boiling. The hot water and cold water taps are separate in the bathroom, where the kitchen has a handle which...

Hot water turns cold [ 1 Answers ]

We have an old furnice (15-20 years old) that I think heats the hot water on demand as we have no hot water tank (apart from the overflow). We use oil as a fuel and have hot water radiators in one zone and baseboards in a second zone. The problem is that when we go to take a shower it starts very...

2 minutes of hot water & then turns cold [ 3 Answers ]

Dear all, I bought a condo a week back and there seems to be this problem of us not having hot water from any of the outlets for more than a minute or 2. Our water heater runs on gas and there doesn't seem to be any problem with the air, which is heating up the house all right. Kindly help!...

HOT WATER for 3 minutes; then turns COLD [ 4 Answers ]

I live in a condo and have an electric hot water heater. Every time I need to wash clothes or use the dishwasher, the hot water never comes out. However, when I turn the hot water on in the bathroom upstairs in the tub, it will be hot for 2 minutes then turn cold the entire time. The hot water...


View more questions Search