    Faulty pressure switch
    I have a Concord 80 Plus Gas Furnace. I had a friend look at it when it was blowing out cold air when turned on, and he said the burners were not kicking on for some reason. When taking a few things apart, he determined that it was due to a faulty pressure switch. When the two wires that attach to the pressure switch are put together the burners kick on. But they have to be reattached each time to keep it running when it shuts off. I want to make sure that the pressure switch is the problem before purchasing a new one?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Oct 30, 2007, 04:30 PM
    Check for a plugged up line going to the pressure switch. If not plugged up it usually means the switch is bad. Is your combustion air blowr working?
    T-Top's Avatar
    T-Top Posts: 1,871, Reputation: 100
    Ultra Member
     
    #3

    Oct 30, 2007, 04:58 PM
    All your doing when you touch the two wires together is bypassing a safety switch. You can blow and suck lightly on the small rubber line going to the pressure switch(disconnect from collector box). You should here it click when you do this. Hook the line back up to the collector box and blow on the line once more to make sure the collector box is clear. If you have a restriction in furnace vent pipe that will keep it from closing.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

No Water Pressure Switch help [ 7 Answers ]

I noticed my water pressure was not as good as it used to be, and that when we used water, I did not hear the switch kick on as it once did, so I went out side and seen that the switch was staying closed, so I turned off the breaker, to see if the switch would kick out and reset its self. Well this...

Continuity of pressure switch [ 1 Answers ]

I am trying to determine if my pressure switch is bad. (Carrier Weathermaker 8000) On a good switch, should the continuity between the posts test open or closed? THanks.

Faulty limit switch? [ 6 Answers ]

Toward the end of a heating cycle, the burners would shut down and the fail code would read "open limit switch". The repairman said the limit switch was faulty and installed a new one a couple of days ago. It seemed to work fine until this morning, and now it's doing the same thing as mentioned...

Limit Switch - Pressure Switch [ 0 Answers ]

Hello Folks, This weekend I've been playing with a heating system at my new apartment and I'm trying to figure out what the different componets do. I kind of followed the circuit but still have some missing links... 1-There are some terminals on the furnace's circuit board labeled LIMIT. The...

Well Pressure Switch Help! [ 2 Answers ]

I have decent pressrue in the house, but I did not hear the pressure switch kicking on and off as it used to. I went out side and checked and the switch points are staying closed, and the pump is running all the time. I can shut off the electric, and open the points by hand, then when I turn on the...


View more questions Search