    100 amp sub panel
    We are going to put in a 100 amp sub panel from a pole barn that has a 200 amp panel. This 100 amp panel will be 125 feet way in another pole barn. My question is what kind of wire do we need if it is going to be buried. This is in Northern Minnesota. Thank you
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #2

    Oct 22, 2007, 03:56 PM
    I would Use 3 # 2's. Could probably go down 1 size with neutral. A #6 for Ground, this would be for Copper.
    I would Use PVC. 2" will not hurt, may help in the future. Trench is the Money.
    Throw in 3/4 PVC conduits also for TV, SAT, Phone, Alarm, Innercomm, 3 Way Switching for lights?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

200 amp panel feeding a 100 amp panel roughly 130' away [ 7 Answers ]

Hi all, We are building a apartment above the garage,my question is what size wire do I need to run from the 200 amp panel to the 100 amp panel roughly 130' away? I want to use aluminum wire as I think copper would be to costly. Thanks for your help in advance, Dude :eek:

100 amp panel [ 1 Answers ]

Hi I am wondering what kind of wire I need for wiring a 100 stablok panel Here's the description I've wired the garage up and I put a 100 panel now I need to bring the wire 180 feet to the house to the main breaker in the house wich the main breaker is 200 amp I have place for a 100 amp...

100 Amp Subpanel from 200 Amp main panel [ 2 Answers ]

I want to install a subpanel to be used to supply branch circuits to a new kitchen, laundry, garage, and some additional lighting and receptacles. The 200 amp main panel is about 50 ft away but because of the obstructions, we'll need about 85 feet of cable to connect the 100 amp subpanel. Since...

Using 100 amp panel on 200 amp service [ 5 Answers ]

I am building new camp at a site that already has 200 amp service. My power requirements are small and 100 amp will be more than sufficient. Is there any reason I cannot hookup a 100 amp panel to the 200 amp meter socket? Not sure is code allows this. I want to use a small 100 amp panel vs the...

100 amp sub-panel [ 3 Answers ]

Can I put a 100 amp sub-panel in my attic? My attic has pull down stairs and is unfinished. I was hoping I can put a sub in my attic to make it easier for numerous runs I have to do on the second floor. I want to be up to code and do not want any issues with homeowners insurance. Thanks, mike


View more questions Search