    KevinC's Avatar
    KevinC Posts: 2, Reputation: 1
    New Member
     
    #1

    Oct 20, 2007, 08:31 PM
    Wire type for service Disconnect
    I am installing an new service disconnect and meter base on the back of my garage/pole building. I have run wire underground from the new meter base to the house to get rid of the overhead and will be replacing the service to the house.

    My question is what type of wire is needed out of the service disconnect (line side) to the weatherhead for the EC to hook up to the incoming line.

    Next question is on the same lines. Going into the house will be a disconnect as it is too far from the main service disconnect. From there to the new breaker panel, which type of wire is to be used. This is a 200A service.

    Thanks
    Kevin
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Oct 21, 2007, 04:45 AM
    You can use 4 wire aluminum URD cable, rated USE for direct burial. You can use a large conduit as a sleeve for extra protection, and under paved areas for easy replacement if needed.

    Or you can use PVC Schedule 40 conduit with all the fittings for a continuous raceway system, and pull aluminum wires with XHHW insulation or THHN/THWN copper wire.

    Inside you can use 4 wire aluminum SER cable.

    For 200 amp residential, you can use 3- #4/0 Al or 3-#2/0 copper. The fourth wire, equipment grounding conductor, can be minimum #6 copper or #4 al.

    Be sure to connect the neutral, equipment ground, and the grounding electrode conductor all together at the main disconnect. The neutral and equipment ground will be separated at the panel.
    KevinC's Avatar
    KevinC Posts: 2, Reputation: 1
    New Member
     
    #3

    Oct 21, 2007, 12:22 PM
    Thank you Mr Russell

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

SPA disconnect switch grounding wire requirement [ 1 Answers ]

I'm installing a 240V/60A SPA approximately 85 feet from the house service panel. I'm going to run 3 individual #6 conductors (THN or better) from the service panel to the SPA GFI disconnect box via 1 inch PVC conduit. The SPA is about 7 feet from the disconnect box. The disconnect box instructions...

200 amp service disconnect [ 1 Answers ]

What type of 200 amp service disconnect ( type 3 ) is better, a fused type or breaker type? Are they both available with a knife switch type handle?

Hard wire 3 wire to 4 wire 220 service [ 1 Answers ]

How do I hard wire my 3 wire (red,blk & bare copper wires) 220vac cooktop to the 4 wire (black/white stripe,black/red stripe, blk/blk & bare alum wires) in the house supply j-box ?

Hard wire 3 wire to 4 wire 220 service [ 2 Answers ]

How do I hard wire my 3 wire (red,blk & bare copper wires) 220vac cooktop to the 4 wire (black/white stripe,black/red stripe, blk/blk & bare alum wires) in the house supply j-box ?

200 Amp Outside Service Disconnect [ 5 Answers ]

I NEED TO KNOW IF A "200 AMP OUTSIDE SERVICE DISCONNECT" IS THE SAME THING AS A "200 AMP OUTSIDE MAIN BREAKER OR LOAD CENTER"? SOMEONE PLEASE HELP ME!! HOME DEPOT WAS USELESS.:confused:


View more questions Search