    Chilled water pumps
    How I can select the pump after I get the flow required and the head
    I have a closed loop system chillers in ground level and 35 floors height
    Are 4 bars enough to start the system which is the head that I calaculated?
    What is system pressure then?
    Do I have to add the vertical height also to the total of the pump pressure?
    The head doesn't represent pressure of the system is that true?
    caibuadday's Avatar
    caibuadday Posts: 460, Reputation: 10
    Full Member
     
    #2

    Oct 20, 2007, 01:15 PM
    Quote Originally Posted by murad79yameen
    how i can select the pump after i get the flow required and the head
    i have a closed loop system chillers in ground level and 35 floors height
    are 4 bars enough to start the system which is the head that i calaculated??
    what is system pressure then??
    do i have to add the vertical height also to the total of the pump pressure?
    the head doesn't represnt pressure of the system is that true?
    4 bar only get you up to 11 floor(max, assumed each fl is 12 ft H), 1 bar= 14.7 psi(g), to pump water up to 1 ft H you needed 0.433 psig. A 35 story building require min 182 psig
    At 182 psig won't be enough because that is only for the vertical lift, you also have pressure loss due to friction loss( piping and associated fittings , your coil and chiller)
    RavenLord's Avatar
    RavenLord Posts: 3, Reputation: 1
    New Member
     
    #3

    Mar 19, 2008, 09:29 PM
    You 7abeebi .
    First of all you have a 35 Floor Building , and what you require is a minimum of 11.5 bar , and several not just one . Always put one on the stand by mode ,

    The pump has to be chosen according to both Horizantal and vertical Pipes , Vertical Pipes are important in your calculation ,
    If you are in the Gulf use grandfos Grundfos | The full range supplier of pumps and pump solutions

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Chilled water pressurization unit [ 3 Answers ]

1- what is the function of the pressurization unit in chilled water system and can the system operate with out it i.e with expansion tank only 2-what the correct arrangement of pressurization unit+expansion tank+air separator.. I mean how these are linked together

Chilled water pump for HVAC [ 15 Answers ]

Kindly let me know what pump I should use for a chilled water close loop system where required flow rate is 102 m3/hr and the max. hight of building is 100 ft.

Chilled water pipe [ 3 Answers ]

I am very new to askmehelpdesk.com. My question is, The building height is 300m. There are 6 chilled water risers going up to 125m height. The chilled water flow rate of each riser as follows. Riser 1 & 2 - 150l/s Riser 3 & 4 - 180l/s Riser 5 & 6 - 100l/s Chilled...


View more questions Search