    Measuring Electric Power
    Using the formula I=P/E will give me amps. Therefore if I have a circuit containing 35W Triphos Lighting Tubes with a 240v supply I should get 0.145amps. Why, when I use a clamp Ameter do I get a much higher reading?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Oct 19, 2007, 03:38 PM
    I tried to find your product, but with no luck. I will guess that this is some sort of HID , High Intensity Discharge, lamp, that uses a ballast to operate.

    The inductance and other losses will draw a bit more current and add to the wattage rating of the lamp. This is called Volt-Amps, other than watts. Watts is for pure DC or AC resistive loads.

    Va includes all the other characteristics of AC power.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #3

    Oct 19, 2007, 06:51 PM
    If it's a like a fluorescent tube the current waveform is from sinusoidal. You will get a closer number if your meter uses TRMS or True Root Mean Squared.

    Power is really the integral of a single cycle of V(t)I(t)dt. It also needs the Root Mean Square thing around it. The rms transformation basically inverts the portion below the axis and averages that result.

    For sine waves it's VI*cos(theta) and this simplifies to VI for AC and DC resistive circuits.
    Credendovidis's Avatar
    Credendovidis Posts: 1,593, Reputation: 66
    -
     
    #4

    Mar 27, 2008, 06:18 AM
    Quote Originally Posted by robkay
    Using the formula I=P/E will give me amps. Therefore if I have a circuit containing 35W Triphos Lighting Tubes with a 240v supply I should get 0.145amps. Why, when I use a clamp Ameter do I get a much higher reading?
    KeepItSimpleStupid touched the answer to your question.
    Older fluorescent tube light systems used a big ballast (coil) to allows the light to ignite while limiting the current through the light (the resistance of the light is very low once ignited).
    Because of that ballast you measure an inductive current. The electric system measures the total system load, not the inductive load. That load is the root of the added squares of the resistive (light) load and the inductive (ballast) load.
    A 35 Watt light system consumes 35 Watt. Not what your meter indicates! No worry!
    ;)

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Heater - Seems to have no electric power [ 27 Answers ]

Hello everyone, I have a rather new (3-4 yrs) Goodman 92 heating system. It was not responding at the thermostat so I tried resetting stuff there, etc. with no result. In checking the heating unit, I see that my Honeywell Enviracare has no power light lit and the heating unit seems to be in...

Electric Power to Outbuilding [ 3 Answers ]

My house has 200 amp service. I am running power to my new shed 250 feet from the house and need no more than 60 amps. What size wire (direct bury) do I need and should I be looking at copper or aluminum? Also, is there a formula to calculate the wire size based on amps, distance, voltage...

$500! Electric bills// power -save 1200 any info? [ 1 Answers ]

I have been seaching for ways to save on electric bill over $500 a month last three months And looks to be that way a couple more. I ran across this Power-Save1200 web-site. Does anyone know if this works? Any other suggestions would be a great help.! going broke!

Power pole that electric company won't fix. [ 3 Answers ]

So I'm helping my friend with this problem. He lives on a lot with a private power pole. Recently it shifted and the meter (which is on the pole) disconnected from the breaker that feeds into his house. So now he is without power, I've contacted a contractor to set the pole straight, but he said...

Kenmore electric dryer/ no power [ 1 Answers ]

I have an electric kenmore dryer, seems like it is not getting power. I have checked the breaker everything is fine there took off the back panel and have tested that it is getting power as far down the hot wire as I can check that leads to the blower motor. Even when you open the door there is no...


View more questions Search