    Eliminate a meter
    In this three story apartment triplex there is three separate meters and three separate 70A disconnect switch (circuit breakers) and from the disconnect power goes to a panel in each apartment. But the building was never zoned for the three apartments. So what the owner wants to do is eliminate one of the three meters and still use the panels that are in the apartments it will just be one panel per floor. What I want to know is can I move the cable from one disconnect to another and change the 70A breaker to 100A.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Oct 13, 2007, 04:50 AM
    Your plan really depends on the total load of both apartments, if 100 amp would be sufficient for both. At least you know you will be limited to 100 amp, if the load is greater then the main will be tripping. Under most conditions, I suppose this would be rare.

    If the plan is to connect all three apartments to one 100 amp main, then this situation is exasperated even more.

    The other issue is how this would be distributed mechanically. Exactly how would the additional feeder cables be connected to one 100 amp main? You may splice all these cables together with a pigtail to each lug, the enclosure will need to be large enough to contain all the cables and splices.

    With the exception of certain perfect conditions, I would not recommend this plan.

    Perhaps some photos of the mains, feeder cables, would help to advise you on this.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Eliminate floor bounce [ 8 Answers ]

The first floor of my 30 year old two story house consists of 5/8 inch plywood on 2 by 8 joists every 12 inches. When I walk around the living room or dining room the glasses etc in the china hutch or bar rattle because the floor is so bouncy. I tried correcting the situation by gluing and...

Bathroom sink odors how to eliminate them [ 2 Answers ]

What's the cause of odors in my bathroom sink that's less then 1 year old, and how do I get rid of them.

Eliminate sexual urges [ 6 Answers ]

Hi all, I am 30 year old guy unmarried. Never had sex. I wish to remain unmarried and get rid of my sexual urges entirely. However, what ever I do should not cause permanent damage, in case I change my mind later in life I myself do not understand what has led to the present state of my mind....

Gfi circuit - can I eliminate one receptacle? [ 3 Answers ]

I want to replace a dual switch/receptacle in the middle of a GFI series - with just a switch (the dual switch/receptacle is not available in the designer color I want). Can I do this and maintain the GFI protection of the downstream receptacles?


View more questions Search