    A/C blower fan won't stop when thermostat is off
    Sorry for the separate thread...
    I had a bad blower fan up in the attic. I ended up taking apart the blower and seeing that the fan was completely disgusting and rusted through. After a very hot weekend without A/C, I took the fan to a parts wholesaler and got a new one. It was harder than I thought to put the motor through the new fan, but after a couple of hours the fan was back in one piece. I set up the system and turned the power back on... The fan was working great...
    Then I turned the thermostat off to turn off the fan... only the fan kept going. I realized the motor had just slower down. The motor is a 3-speed. I shut off the power at the fuse box, and of course this shut down the fan.
    I'm very confident I rigged the fan the same way it was before- I only separated three cables from the motor, and then put them back (red to blue, black to black, and yellow to yellow). What happened?? Please help!
    J Costa's Avatar
    J Costa Posts: 88, Reputation: 9
    Junior Member
     
    #2

    Oct 2, 2007, 05:14 PM
    Sounds like it would be your relay is stuck. What made you take the fan apart in the first place? What I mean is was there a problem before that made you look at the fan?
    gbwillner's Avatar
    gbwillner Posts: 27, Reputation: 1
    New Member
     
    #3

    Oct 2, 2007, 05:25 PM
    Quote Originally Posted by J Costa
    sounds like it would be your relay is stuck. What made you take the fan apart in the first place? What I mean is was there a problem before that made you look at the fan?

    Thanks for the response.

    I took the system apart because the blower fan became disconnected from the motor- it was rusted through. I replaced the fan, and put the blower back together.

    Actually, now I have an additional problem. The condenser, compressor, capacitors, and blower all work. However, the air that comes out is not very cold. I noticed that the freon "cold" line coming into the house is not very cold either, although the "hot" one is. There is condensation on the condenser and air coming out of all the vents. Any ideas??

    Thanks
    J Costa's Avatar
    J Costa Posts: 88, Reputation: 9
    Junior Member
     
    #4

    Oct 2, 2007, 05:59 PM
    You are probably low on refridgerant if the low side line, the fat line is not cold and has no condensation on the line outside and you say the compressor is working that is probably your problem.
    T-Top's Avatar
    T-Top Posts: 1,871, Reputation: 100
    Ultra Member
     
    #5

    Oct 2, 2007, 06:06 PM
    You said the blower slowed down when you shut it off at the thermostat. If its electric strip heat you may have a heat sequencer stuck. The blower relay will energize the high speed for cooling when the relay drops out the low speed is controlled by the heat sequencer. You said the air was not that cold in a/c mode sounds like a strip may be stuck on to me.
    gbwillner's Avatar
    gbwillner Posts: 27, Reputation: 1
    New Member
     
    #6

    Oct 2, 2007, 06:10 PM
    Quote Originally Posted by T-Top
    You said the blower slowed down when you shut it off at the thermostat. If its electric strip heat you may have a heat sequencer stuck. the blower relay will energize the high speed for cooling when the relay drops out the low speed is controlled by the heat sequencer. you said the air was not that cold in a/c mode sounds like a strip may be stuck on to me.

    Thanks!
    How do I fix this?
    T-Top's Avatar
    T-Top Posts: 1,871, Reputation: 100
    Ultra Member
     
    #7

    Oct 2, 2007, 06:22 PM
    If it's a bad sequencer you can take the red blower wire off the sequencer and tape it off. (turn power off first!). If you have a heat strip that hooks up at the same point you need to disconnect it to and tape off. This will get you going until you can get a new part. It's a common part and not expensive. I hope it works out for you.
    gbwillner's Avatar
    gbwillner Posts: 27, Reputation: 1
    New Member
     
    #8

    Oct 2, 2007, 08:00 PM
    Quote Originally Posted by T-Top
    If its a bad sequencer you can take the red blower wire off the sequencer and tape it off. (turn power off first!). If you have a heat strip that hooks up at the same point you need to disconnect it to and tape off. This will get you going until you can get a new part. its a common part and not expensive. I hope it works out for you.

    Thanks!!

    I ran the AC (even though it wasn't cold) just to de-humidify the house. When I went back up to the attic (where the blower/furnace is) I smelled something burning. I touched the back plate of the heating elements and noticed they were really hot.

    I guess the problem was the blower and furnace were both permanently "on" for whatever reason. I took the leads off the heating coils and the A/C is now running better than ever.

    If anyone knows how to replace this part (or knows a good resource) plase let me know.

    Thanks again!

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Thermostat Q - Blower Does Not Turn ON in FAN Auto Mode [ 10 Answers ]

I just installed a NOMA 7-day programmable thermostat for an electric furnace/AC system (ceiling unit). I believe the wiring (5-wire) is correct. When I set it to COOL with Fan set to AUTO, it turns on the A/C and the fan automatically. Good. But when I set it to HEAT with Fan set to AUTO,...

How to Wire a Thermostat to blower fan for alternate heat source [ 5 Answers ]

Hello all I just built a plenum around my coal stove and I need to wire in a stat , limit switch to run a blower fan . Thanks Steve PS I have all the parts off and hot air oil furnace.

Service blower won't stop [ 4 Answers ]

The other night I woke to the sound of the service air blowing but no compressor. The blower would not shut off nor could I turn it off at the thermostat-had to turn it off at the unit. Code light is flashing "6" which is reverse polarity or bad/weak ground. We had some good thunderstorms...

Blower won't stop [ 1 Answers ]

My carrier furnace blower motor runs even when the thermostat is turned off burner won't lite up please help we are cold thanks.

Blower does not stop? [ 4 Answers ]

I went on vacation for 10 days. Before I left, I turned off my unit from the termostat, letf the unit on OFF and fan on Automatic. Also turned off the pilot on my gas water heater. When I got back, the blower which is part of the furnace was running! who knows for how long. The house was at 90...


View more questions Search