    200 amp cables
    Is there a maximum length for a electrical line from my 400 amp service panel to a 200 amp service panel in my detached garage. I would like to run the cable through the attic and outside then to the garage and the 200 amp panel. The detached garage is approximately 10 feet from the house.
    Thanks
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Oct 1, 2007, 12:22 PM
    To properly calculate voltage drop, three variables are needed,one, the load in amperage, two, the entire length of the cable from point to point, and three, the size wire planned to be installed.

    Since the building is only 10 feet away from the main building, there is no concern for worry as long as the feeder is no smaller than #4/0 aluminum or #2/0 copper.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Running 100 amp service panal 200 ft away from main 200 amp service [ 4 Answers ]

I am looking to find out how big the wire needs to be to carry the load. This will be a 100 amp service coming from a 200 amp main . It will need to travel 200 to 250 ft underground to a barn. If some one could help me that would be great thaxs)))

400 amp service, 2 200 amp panels, 320 amp meter socket [ 10 Answers ]

Hi, this is my first post here, but I have been reading a lot and have already learned a bunch. I want to thank TK already and hope you reply to this. I am in the process of designing my electrical system for my new home. I have some electrical experience, but am by no means a pro. I am...

400 amp service with 2-200 amp panels & 320 amp socket [ 6 Answers ]

Hi TK. I am running 400 amp service into my new contruction home. The electric compnay is running a single 400 amp line to the meter. I have to split it to the two panels at that point. You had told me once before that I need a 320 amp meter socket and then run 2-200 amp lines to the separate...

2 200 amp disconnects and a 200 amp meter [ 3 Answers ]

On a new house I have 2 200 amp panels on the inside. What will be the best way to hookup the 2 200 amp outside disconnects and meter to look decent for the house?:o

200 amp service with a 200 amp outdoor breaker [ 1 Answers ]

I need to know how to wire a 200 amp outdoor breaker enclosure.I have 4/0 scu cable for my service head to the meter,and 4/0 scu from meter to breaker enclosure.Then from the breaker enclosure I have 4/0 ser cable to my panel.What is the proper wiring method in the enclosure,please help.


View more questions Search