    Fire Damper
    In HVAC Clean Room FIRE DAMPER will be installed in SUPPLY DUCT or in RETURN DUCT?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Sep 27, 2007, 02:58 AM
    Both, along with duct smoke detectors in both supply and return ducts.
    rajuas100's Avatar
    rajuas100 Posts: 10, Reputation: 1
    New Member
     
    #3

    Sep 27, 2007, 03:24 AM
    Quote Originally Posted by tkrussell
    Both, along with duct smoke detectors in both supply and return ducts.

    If we want install FIRE DAMPER choose any one side of supply or return duct?.

    Then in which duct fire damper to be installed?.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Sep 27, 2007, 04:14 AM
    The clean rooms and data centers I have done, have dampers in both ducts.
    caibuadday's Avatar
    caibuadday Posts: 460, Reputation: 10
    Full Member
     
    #5

    Sep 27, 2007, 04:19 PM
    Quote Originally Posted by rajuas100
    If we want install FIRE DAMPER choose any one side of supply or return duct ?....

    then in which duct fire damper to be installed?...
    If you have to choose one then it is the supply side
    The purpose of the FS damper is to prevent smoke and fire to spread, in case there is a smoke or fire in the areas near by (same floor, one floor above/below) the ahu must be automatically stop... if the ducts( SA/ RA) penetrated a fire rated wall it best to put FS damper... but then it up to your local government to tell you where to put the FS damper, but it will need at least one, at the supply side

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

How do I replace the damper [ 2 Answers ]

I have an old jenson wood boiler, probably 20 + tears. Works great but the flu fell out of it. How do I find replacment parts.

Fireplace damper [ 2 Answers ]

Hi,this is whisky4,I was wondering if there is ratio that you use to determine the size and how much you can close up the throat of a fireplace to make it more efficentor do you just play it ear,i.e. close it up until it smokes then back off,thank,s

I'm on fire! [ 7 Answers ]

Ok well I'm not on fire my forehead is.. >!! What do I do if I burned my forehead with my hair straightner but I can't find any aloe!. I NEED HELP SOON!!

Belimo Damper Actuator [ 1 Answers ]

On a Belimo Damper Actuator AMB 24-3, the black wire is the common wire and the white and red wires are used to determine the direction the actuator runs. Is this correct? How does a person test a wire to find out if it is the common wire?

Fire [ 3 Answers ]

I had a fire in my apartment on July 27. I didn't have renters insurance. When I applied for the Fire Marshall report it stated that it was inconclusive (they could not determine who's fault it was), now my question is can I sue the management company for compensation of lost items, i.e furniture


View more questions Search