20 Amp Outlets
I am finishing off a basement. I ran 20 amp 12-2 wire with ground for the outlets and 15 amp 14-2 wire with ground for lights.
1) Can I use 15 amp outlets for the 20 amp outlet run? Or does that overload the outlet?
2) What is the functional difference between 15 amp and 20 amp outlets?
3) Can I run a leg off a 20 amp outlet to a remote 15 amp light without any electrical danger? Do I use 12-2 or 14-2 for the leg to the light?
|
|
 |
Printers & Electronics Expert
|
|
Sep 16, 2007, 06:47 PM
|
|
Personally I would only use 12/2 with 20 amp outlets.
1 - - If you use a 15Amp rated outlet on a 20 amp rated line, you must use a 15Amp breaker and limit the electrical load to a max of 15 Amps.
If you use a 20 Amp Breaker with a 12/2 20 Amp wire you should not have any problems with the load on the line as long as the max load is limited to 20 Amps.
2 - - 5 Amps more of safe circuit current.
3 - - Again the limitation is the Amperage draw of the total circuit.
Electricity is a "Demand" product. Just because you put a lamp on a 15 Amp Circuit does not mean the lamp itself will draw 15 Amps every time it is on. If that were true, then the amount of circuits that would need to be run for an average size house would be staggering.
Then there is this little problem of the NEC Code. You must meet the requirements of the NEC Code to be compliant. For example, you cannot use 14/2 to carry 20 Amps. In theory, the wire would overheat and melt the insulation or even shear the line.
Also, you cannot use a standard wall receptacle near water. The Nec Code calls for the use of GFCI outlets near water.
There are several electricians on this site and since I am not one of them, I will defer to any of their responses.
|
|
 |
Uber Member
|
|
Sep 17, 2007, 07:44 AM
|
|
(2) the 20 AMp outlets accecpt 20 A 120 V plugs and 15 A 120 V plugs. On a 15 A receptical both slots are verticle. On the 20 A, one side has both a verticle and a horizontal slot. The 20A outlet can carry 20 Amp safely. The 15A outlet can carry 15 Amps safely.
|
|
 |
Full Member
|
|
Sep 17, 2007, 07:09 PM
|
|
1) Can I use 15 amp outlets for the 20 amp outlet run? Or does that overload the outlet?
Table 210.21(B)(3) in the NEC allows a circuit rating of 20 amps to use 15- or 20-amp receptacles. From the commentary”…two or more 15 amp receptacles or duplex receptacles are permitted in a 20 amp general purpose branch circuit.” This actually derates the circuit based on the 125% rule. The breaker rating doesn't overload the outlet, the total current draw of the item(s) plugged in the outlet overloads it.
2) What is the functional difference between 15 amp and 20 amp outlets?
See KISS explanation.
3) Can I run a leg off a 20 amp outlet to a remote 15 amp light without any electrical danger? Do I use 12-2 or 14-2 for the leg to the light?
15 and 20 amp branch circuits can supply lighting, but you must use 12-2 to the lights. NEC 210.23 and 210.24 set the requirements. If the circuit supply's both a light and two or more fixture outlets, then the circuit must have the same rating as the breaker-if using a 20 amp breaker all branch circuit wire must be #12.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
400 amp service, 2 200 amp panels, 320 amp meter socket
[ 10 Answers ]
Hi, this is my first post here, but I have been reading a lot and have already learned a bunch.
I want to thank TK already and hope you reply to this.
I am in the process of designing my electrical system for my new home. I have some electrical experience, but am by no means a pro.
I am...
400 amp service with 2-200 amp panels & 320 amp socket
[ 6 Answers ]
Hi TK. I am running 400 amp service into my new contruction home. The electric compnay is running a single 400 amp line to the meter. I have to split it to the two panels at that point. You had told me once before that I need a 320 amp meter socket and then run 2-200 amp lines to the separate...
220 Outlets & GFCI Questions
[ 3 Answers ]
I'm wanting to add some 220 outlets in the garage to run my woodworking equipment, and I have a couple of questions. First, can I run one 220 circuit with approximately 4 plugins on it? Only 1 piece of equipment will ever be used at one time (or does this violate code? ). Also, I'm under the...
Outlets for GFI circuits - bath & kitchen
[ 3 Answers ]
Hi - 2 questions:
1. I'm adding whirlpool bathtub as part of a remodel job. I've got 2 20amp dedicated lines, 1 for the pump, 1 for the heater. Each of these has to be on a GFCI breaker in the main panel, do I just use a regular receptacle under the tub enclosure, or is there a special...
View more questions
Search
|