    Sizing of ground wire
    Hello, I need to know how to figure the sizing of the ground wire for a 150a 3 phase sub panel, I figures 1/0 wire, but what sizw ground? & how do I find it out myself next time?
    Many thanks, Julie
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Sep 12, 2007, 02:15 PM
    You can review the National Electric Code by a link found in the Read First sticky note of this forum. There are also instruction to get to the actual document.

    In Article 250 find Table 250.122 that lists the min size equipment grounding conductor. You will find that a circuit protected at 150 amps will need a #6 copper or a #4 aluminum. Use the 200 amp rating, as this exceeds 150 amp.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Earth wire cable sizing [ 3 Answers ]

Hi , Im mike, 29 years old, I live in Mauritius. I would like to know how to size my eathing wire since my supply wire is 6 mm2. Thanks

Wire sizing and conduit sizing [ 8 Answers ]

I am looking for confirmation on some of the info I have found and answers to a few missing pieces. This is regarding wire size and conduit size for service conductors from the meter to the breaker panel (about 30 ft away). Wire Size: 125A service needs #2 copper or 1/0 aluminum -- #6 copper...

Proper wire sizing? [ 3 Answers ]

We are re-routing the supply line to our pump house, where there is an extension panel with 30A 220V (pump controller) and 15A & 20A 110V breakers. It's about a 60' run from the 200A main service in the house, being placed in conduit 2' underground. The wire in place is newer 10 gauge solid copper....

Ground wire [ 1 Answers ]

At what point do you have to use a ground wire in lu of metal conduit, Or do you?

Wire sizing for sub panel. [ 1 Answers ]

Thank you for the response on my sub panel questions. I finally found a slim line breaker which will work in my main panel. I can now consolidate two breakers to give me room for a 100 ap breaker. This breaker will feed the sub panel in my workshop. I plan on placing a 100 amp sub panel in the...


View more questions Search